Doing an EICR in a commercial building, taking on the advice from last post I was doing the IR individually rather than across the entire board, circuits wired in singles so had to locate the correct neutrals when I found this on 2 circuits, wondered if anyone had come across this before:
With Neutral disconnected I measure 400v between N & L1/L2, 0v between N & L3 so I presume its a L3 conductor, I also measure 230v between N & E
Reconnect the neutral and I measure 230v between L1/L2/L3
Need to look further into it but any thoughts appreciated
With Neutral disconnected I measure 400v between N & L1/L2, 0v between N & L3 so I presume its a L3 conductor, I also measure 230v between N & E
Reconnect the neutral and I measure 230v between L1/L2/L3
Need to look further into it but any thoughts appreciated