What about the incoming protection for the installation?Ironically you mention fuses (neozed etc). Well, in five years time, only place you will see a fuse in this country is likely to be a museum
Discuss Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net
A 63 amp mcb for a standard 12kva supply. As of February this year, new regs stipulate that now becomes a double pole 63ampWhat about the incoming protection for the installation?
That is interesting. Certainly makes it easier to disconnect the CU supply to do any work!A 63 amp mcb for a standard 12kva supply. As of February this year, new regs stipulate that now becomes a double pole 63amp
Of Course, but I do believe that the majority of rural ROI properties are still TT, but I have no facts to back that up except for the lodge I stay at in Enniskillen.I think ROI is mostly TN-C-S now so no need for an incoming RCD. In any case there has to be some form of over-current protection so it would need to be an RCBO here.
Yes.The difference between it and the other mcb, s is that it may be a "C" instead of a"B" type if the supply characterises allow. You raise an interesting question in my mind though as to why it can be a regular MCB instead of an MCCB and offhand I suspect it may have to do with the DSO, s protective fuse in the meter cabinet. Must look into that.That is interesting. Certainly makes it easier to disconnect the CU supply to do any work!
It is just a regular MCB (not MCCB)?
Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net