A 63 amp mcb for a standard 12kva supply. As of February this year, new regs stipulate that now becomes a double pole 63amp
That is interesting. Certainly makes it easier to disconnect the CU supply to do any work!

It is just a regular MCB (not MCCB)?

Typically the use here of a BS88 fuse gives selectivity with many down-stream MCB characteristics as well as far higher braking capacity and fault current-limiting characteristics, but probably in most cases they are not essential (though some cities' supply points can deliver over 10kA PFC).
 
I think ROI is mostly TN-C-S now so no need for an incoming RCD. In any case there has to be some form of over-current protection so it would need to be an RCBO here.
Of Course, but I do believe that the majority of rural ROI properties are still TT, but I have no facts to back that up except for the lodge I stay at in Enniskillen.
 
I think rural is often TT (or to all intents and purposes, TT) in most of the world, as you don't easily get a low R earth and you might want to avoid the transformer's LV one as it may be too close to any HV side earth.
 
That is interesting. Certainly makes it easier to disconnect the CU supply to do any work!

It is just a regular MCB (not MCCB)?
Yes.The difference between it and the other mcb, s is that it may be a "C" instead of a"B" type if the supply characterises allow. You raise an interesting question in my mind though as to why it can be a regular MCB instead of an MCCB and offhand I suspect it may have to do with the DSO, s protective fuse in the meter cabinet. Must look into that.
Regarding the DP main switch, well that is simply a gift for a number of reasons but chiefly we can now do IR tests effortlessly on non - rcd protected circuits on TNC-S systems without having to first disconnect the main Neutralising earth from the bus-bar.
 

Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock