Search the forum,
Discuss help needed with a customer? in the Commercial Electrical Advice area at ElectriciansForums.net
Better to get it right then mess it up a tony! Awesome comment there.
Smiffey, id suggest you start with an Assessment of the General Characteristics of the Installation, with what you have put forward you will mess it up.
A 100 mA RCD incomer, they will be happy with you when everything comes to an abrupt stop.
Whats the supply type, earthing arrsangements, bonding requirements etc?
Lightning protection, surge protection?
Whats level of fault current at origin?
EFLI at origin?
Protective device at origin?
What external inlfuances exist?
What installation method will be used?
What sort of factory is it a P.f of 1, a purly ressitive installation?
Type of Lighting, Heating, Machines etc?
Level of Harmonics?
Maximum Lenght of circuits includuing Final Circuits?
An assesment of Maximum Demand?
Future Expansion ?
Risk assements?
This list isnt exhaustive, but give an indication of where you need to start.
You can then move on to Designing the circuits so that they can comply with BS 7671 and you have a happy customer.
I've given him a list of bits required including the 25mm 5 core swa,
Why on earth are you asking him to supply a 5 core SWA cable?? A 4 core SWA cables armouring, will be more than capable of providing this cables CPC requirements....
well if you ask me £650 for cable at that length and to have 100A per phase is nothing yes you could use smaller cable but protection device will change... you are the spark and he seems a pratt.
The jury is still out on that one.
From what's been said so far I'm not convinced. To set out with a design current of 100A when it's known the service head is only 100A this whole saga is a farce.
Now if the head was to be uprated then things make sense. Mind you 5 core still doesn't make one iota of sense.
Reply to help needed with a customer? in the Commercial Electrical Advice area at ElectriciansForums.net
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
4K
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Hello everyone, I have recently qualified, though yet to start practising, as an electrician. I have noticed, at my home, the tails from the...
11K
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Hi folks, I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right... The circuit will be part of a 3-ph...
