A

ample current

Can some one help, i have been asked about an immersion heater which stopped working so she pressed the reset button on the temperature control, which worked for a while but now the timer has burnt out, any ideas what i should look be looking for when i go round to look at it. would a fault in the element cause this. and what would be the best way to test if the elem ent was at fault. I have a megger 1730 tester so could i use this to check the element. I am new to this especially heating.

Thanks in advance

Mark
 
element should read about 20ohms L/N. then IR test to E. if any doubt, replace. if OK, could be timer has just given up the ghost, or a poor termination has caused overheating. make sure a replacement timer is suitably rated for a 3kW load.
 
Thanks :icon14: if it doesnt read 20 ohms is it likely to be a higher reading or a lower one ? and I take it you mean an ir test on the whole immersion heater circuit.
 
Last edited by a moderator:
Thanks :icon14: if it doesnt read 20 ohms is it likely to be a higher reading or a lower one ? and I take it you mean an ir test on the whole immersion heater circuit.
If it reads higher (a lot higher)(using low ohm setting not IR) then its means its open circuit, element broken.. For IR you wana test the element to E as you could still have a 20ohm reading across L and N making it look ok, but a pin hole in the element shorting to E so test L-E at element..
If all reads out ok, I would fit new stat and time clock..
If heater looks down, then get replaced, fit time clock..

PS your reading may not be esactly 20 ohm.
 
Last edited by a moderator:
i tested the element L-N and it read about 18.5 ohms, didnt check L-E across the element, and i take it ir means insulation resistance test.
The time clock had burnt on the load side on the live conductor at the connector.
I have to go back tommorow to install new cable from heater to timer so do I test using insulation resistance test (500v dc) across the terminals of the element (L-E) whilst its disconnected from the circuit and this should be a very high reading?
Thanks in advance
Mark.
 
Last edited by a moderator:
Yep You got it.. 18.5 ohms is fine. but its best to do IR (insulation Resistance) from L or N of the element to E and as you say it should be a very high reading, if not >999
 
The time clock had burnt on the load side on the live conductor

sounds more like the connection was loose and caused the damage, rather than an element problem. if there is an rcd in circuit, then a poor IR of the element would have caused it to trip.
 
You know i cant remember if there was an rcd on the cu or not now.... must pay more attention, the circuit is protected by a 16amp CB which was off when i first looked at it. I did an ir test across L-E and N-E both were >999 and the circuit to the outlet from the cu read >999 also. I thought it was a dodgy connection also when i saw the burn marks on the terminal.
 

Reply to immersion heater timer problem in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
217
Hi I have a Corby 7700 trouser press it is a 220w model, 3 years 10 month old. On Friday it stopped working, so I took it to the garage ready...
Replies
1
Views
740
There was always talk of teleswitch transmitters being switched off. Does anyone know if that is a thing, or whether it’s been done? I was at a...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock