Clive: none of it is rocket science really, I just think I'm missing something. Looks like what I'm missing is that everyone else is opening up the DB and disconnecting the live conductors for the circuit purely to do IR testing. Which kinda surprises me on a small MWC job but if that's what you have to do it's what you have to do.
 
Clive: none of it is rocket science really, I just think I'm missing something. Looks like what I'm missing is that everyone else is opening up the DB and disconnecting the live conductors for the circuit purely to do IR testing. Which kinda surprises me on a small MWC job but if that's what you have to do it's what you have to do.

Correct. Unless you take the cover off the CU and disconnect the L & N you won't get an accurate reading.
 
Which puts test voltage E-N across the entire installation (maybe damaging stuff), and hence potentially up to L through connected equipment elsewhere in the installation (damaging more stuff)? Unless you disconnect N for the circuit at the DB? or leave the fuse in/MCB close and (L+N)-E test the entire installation?

i think it mentions it in the onsite guide.

you link l+n together and test to e

(l+n to e)

for transformers e.g. selv+pelv circuits like lighting in bathrooms.


it should be perfectly safe to do this at 250v
 

Reply to Insulation Resistance Test For Minor Works in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
633
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
667
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
702
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
950
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock