Discuss Insulation resistance testing with no cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Even with the lack of a CPC on any particular circuit I would still be testing between L-E and N-E. When conducting IR tests it's called earth for a reason, we're not meggering the CPC, we're meggering the earth, ie. from the line conductor to the earth bar or MET and the same for the neutral conductor. What if somewhere on a circuit with no CPC the cable has been damaged enough through whatever means so that one or other of the conductors are in connection with an exposed or extraneous conductive part? Or what if there's a nice fat screw through the cable linking it to another circuit? In my humble opinion, there's a multitude of reasons why we should still be conducting the IR tests as required.

I totally agree. However testing L-Cpc and N-CPC doesnt test the lighting circuits does it if there is no cpc. L-N is the only test which can prove the condition of the cable in this case..
 
I totally agree. However testing L-Cpc and N-CPC doesnt test the lighting circuits does it if there is no cpc. L-N is the only test which can prove the condition of the cable in this case..

If you read my post again you will see that I made a clear distinction between a cable's CPC and Earth in general. When IR testing a cable with no CPC, as well as the obvious L-N test you would carry out on the cable, you should also be carrying out L-E and N-E. Imagine one scenario; the cable has been damaged and the line conductor is exposed and resting neatly on a hot water pipe. How will just a L-N IR test pick this up?
 
If you read my post again you will see that I made a clear distinction between a cable's CPC and Earth in general. When IR testing a cable with no CPC, as well as the obvious L-N test you would carry out on the cable, you should also be carrying out L-E and N-E. Imagine one scenario; the cable has been damaged and the line conductor is exposed and resting neatly on a hot water pipe. How will just a L-N IR test pick this up?

Ah me sees, It wont. Sorry I assumed that you meant this was replacing the L-N test.. N- earth is allways done globally (for me) as it takes less time than doing individually. Only if the reading was less than 2 meg then id be testing individually..

Normally for CCU change and a load of lamps then L/N - Cpc is done globally a) When pricing up and b) When its finished..
 

Reply to Insulation resistance testing with no cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
582
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
992
I am self-teaching fault-finding and testing, but I can't wrap my head around insulation resistance tests. From my understanding you send 500V for...
Replies
14
Views
6K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock