If a cast iron internal drain pipe terminates outside into a clay drainage point is this still classed as extraneous conductive part.

I am being super careful as an NICEIC inspector had me box off a soil pipe on a PME system earlier last month and dont want to come a cropper again.
 
The drain pipe being conductive and internal to the property then means that it would also have to be able to introduce an earth potential (or other potential) into the property to be considered an extraneous conductive part. Because the conductive part goes outside and connects to a non conductive part, so long as the internal drain pipe does not go out underground as usual, then this should not be an extraneous conductive part and in accordance with the 18th edition statements would not require bonding as there is an insulating part before it reaches the earth.
If the drain pipe exits the property underground and then joins on to a clay pipe then earth potential could be introduced and the resistance to earth should be tested to classify if it is an extraneous conductive part or not.
 
Perhaps that bonding pic might be useful. It shows a metal gas pipe exit the building but not needing bonding because it can't introduce a potential.

IMG_1167.JPG
 
Last edited:
Does beg the question of how you would actually bond to a cast iron soil pipe? Not sure I would want to drill in to one and they are usually heavily painted or rusty on the outside.
 

Reply to Internal drainage pipe help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. The toilet is connected into a cast iron waste/soil pipe O.D. 150mm. Apparently, this is an extraneous conductive part and is thus supposed...
Replies
26
Views
8K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K
my lights are dimming everytime an appliance turns on in my appartment and the shared area of the basement next to it. my fridge causes a moderate...
Replies
6
Views
1K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock