He had six years to do it, so no rush !!What do you mean by loose trunking? Is it not secured to the wall? If not then can you just glue it?
I expect you can just glue it. I rent the house. But the electrician is quoting for work as a C2 and my question is whether it should be graded C2 or C3
Well I don't argue with that. But nonetheless I would like some advice about this coding. The trunking is not hanging off its just not attached solidly to the wall. By grading it C2 the electrician does not pass the EICR and I have to pay him to come back. I am looking for guidelines on this gradingDoesn't matter what code, just get it secured. Take less time than finding out what the code should be!
There was a change in the 18th edition, associated with premature collapse of wiring, under this all cables must be properly secured with fire resistant fittings (or other physical means), if this is not present, then it's a C2.
Just gluing it will not satisfy the regs.
No.Would that only apply to a new installation ?
When was the 18th edition brought in. This may explain the change in grading. Interestingly though the electrician who did the original EICR told me that it was not necessary to do anything. It looks quite stable to meWould that only apply to a new installation ?
There was a change in the 18th edition, associated with premature collapse of wiring, under this all cables must be properly secured with fire resistant fittings (or other physical means), if this is not present, then it's a C2.
Just gluing it will not satisfy the regs.
May sound a bit harsh here but....if you are renting the place what do you care about c2 c3 et all?
Thank you for thisWhile opinions and advice differ and there is a degree of judgment in all cases, the best and most accessible guide to EICR coding is probably the Best Practice Guide #4:
https://www.electricalsafetyfirst.org.uk/media/2149/bpg4-1.pdf
Completely understand that mate, I’ve rented in the past just curious as to why so concerned....I’m with you for a decent landlord idve just stuck down and if I liked the client idve made good of whilst doing the EICR so it was never an issue ?I rent a house out and take good care of it. Not all landlords are bad.