incorrect an MCB is an overload device and will operate you can have a maximum value of 200 ohms with an earth spike and the installation has to be protected by an RCD so any earth leakage above 30 ma will cause the RCD to trip ,
 
Last edited by a moderator:
In a tt system? The earth spike is Reading greater than 50 ohms so clearly the mcbs won't make their rated disconnection times. Waste of time?


not very familiar with tt systems but obviously the loop-impedance is way too high for any automatic disconnection of earth faults by mcbs

so rcds will be required
 
In a TT, short circuit protection is by the mcbs
They cant fullfill disconnection times with the higher rod reading for earth faults ,so an rcd does the job
The loop impedence test passes a high current through the earth path to determine a sound low enough reading to operate that rcd,without the test,we cant be sure of the reading or the earth integrity

We could forget the loop impedence test and measure the rod the proper way though
 
how do we measure the earth rod and which method?

The full method is to use a three terminal earth rod tester with two temporary spikes, a current spike and a potential spike. You place the current spike at least ten times the length of the rod away (so for an 8ft coupled rod that's roughly 30m away) and take three measurements, one with the potential spike halfway between the rod and the current spike, another 10% of the distance away from the current spike towards the rod and then a final measurement 10% of the distance away from the rod towards the current spike. The tester then gives you an average value of the three readings taken.

Most of us however will just use our MFT to obtain an Ra value using the loop setting.
 
When using the spike method on an existing installation, how are you meant to know how long the rod is without pulling it out of the ground and probably ruining what could have been a good reading?
 
Yes, as Archy said, look at the install cert, in larger installations the information will definitely be there.

If it's a smaller install and no cert then if it's a twig then it's a four footer, if it's a 5/8" then assume it's a coupled eight footer.
 
I wouldn't ever go shorter than 30m for the current spike, and normally it would be 50m for small commercial/domestic installations where possible!!
You can also use a dedicated Earth Tester in place of a loop tester at the service cut -out MET, using two leads!!
 

Reply to Is there any point testing earth loop impedance in the Australia area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
580
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi everyone, I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth...
Replies
14
Views
2K
Hi I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in...
Replies
30
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock