Discuss leakage in the UK Electrical Forum area at ElectriciansForums.net

i=p/u

-
Arms
Reaction score
801
got a call on Saturday to say the newish washing machine is blowing the trip. when i had nosey around swapping leads and whatever i tried still tripping when starts a cycle.

its a tt installation with a ze of 14 ohms , insulation resistance of machine was as follows
l-e 1.3 M/ohms
n-e 12 M/ohms

earth continuity from plug to metal part of machine was 1.6 ohms

what i thought was an rcd is actual a voltage measuring device, apparently were installed before rcd came about , had no rating on it but has a yellow test button.

what else can i try or if i ring an appliance engineer what will he tell me. or what will he do.

thanks if your full of knowhow. im all ear or eyes
 
start by replacing that VOELCB with a RCD. then take it from there.
 
only get as far as page 3 all time..

.. need to clamp meter to measure earth leakage then can change device accordingly ..with a ze of 14 ohm i can get away 100mA - 500mA

would these devices be more sensitive than rcds?? id say no. but can somone explain how they work
 
you should be installing a 30mA RCD anyway. but, yes, by all means check installation leakage or global IR test before fitting RCD or you might end up spending an extra day sorting out problems which you haven't allowed for in your quote.
 
only get as far as page 3 all time..

.. need to clamp meter to measure earth leakage then can change device accordingly ..with a ze of 14 ohm i can get away 100mA - 500mA

would these devices be more sensitive than rcds?? id say no. but can somone explain how they work

Well if there is a Voltage trip chances the fuseboard isn't 17th compliant?
If I were you I would be giving the customer two choices - direct replacement with 30ma rcd (not recommended)
Fuse board upgrade.
then fix any problems like washing machines.

Voltage trips operate when the touch voltage rises above 50V (unless I'm mistaken)
but are unreliable due to parallel paths making them inoperative.
 

Reply to leakage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
619
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock