Hi everyone,
Hope your all ok and busy busy !!!
Just got back from a callout. Lady has had a chandelier type fitting just put up on her ceiling with 20 of those small 20w lamps inside it. Also she has had 4 new wall lights put on as well (100amps each, the kind of lamps that you fit onto the motion detectors, long type ).
Anyway, her builder switches on the lights and the mcb trips, reset it, all ok, switch on lights, fine, switch off and mcb trips again !!
I went to have a look, the board is a Square D type board, 3 phase (these are duplex flats in Canary Wharf, approx 10 years old ).
Just by chance I had 1 x B type 10amp and 1 x 16amp C type Square D breakers in the van. The board is all C type by the way. I put on the the B type 10amp, thinking about maybe a surge when the lights are switched on (especially the massive chandelier type one ), The lights come on fine, go to switch off, the mcb trips. Reset it, switch on the mcb trips. So I put i the 16amp C type and all is fine !! Switch on ok, switch off ok, switch on again ok (2 way switch).
Do you think, as do I, that its a surge thats causing this ??? Checked continuity of earth in lights and did R1 + R2, all ok, insulation resistance all ok ??
I think I may order her a 10amp C type mcb, as the 16 may be too high ??, but in the consumer unit, the wiring is 2.5mm?
Any suggestions or advise?
Thanks for reading and have a great week everyone,
Sav
Hope your all ok and busy busy !!!
Just got back from a callout. Lady has had a chandelier type fitting just put up on her ceiling with 20 of those small 20w lamps inside it. Also she has had 4 new wall lights put on as well (100amps each, the kind of lamps that you fit onto the motion detectors, long type ).
Anyway, her builder switches on the lights and the mcb trips, reset it, all ok, switch on lights, fine, switch off and mcb trips again !!
I went to have a look, the board is a Square D type board, 3 phase (these are duplex flats in Canary Wharf, approx 10 years old ).
Just by chance I had 1 x B type 10amp and 1 x 16amp C type Square D breakers in the van. The board is all C type by the way. I put on the the B type 10amp, thinking about maybe a surge when the lights are switched on (especially the massive chandelier type one ), The lights come on fine, go to switch off, the mcb trips. Reset it, switch on the mcb trips. So I put i the 16amp C type and all is fine !! Switch on ok, switch off ok, switch on again ok (2 way switch).
Do you think, as do I, that its a surge thats causing this ??? Checked continuity of earth in lights and did R1 + R2, all ok, insulation resistance all ok ??
I think I may order her a 10amp C type mcb, as the 16 may be too high ??, but in the consumer unit, the wiring is 2.5mm?
Any suggestions or advise?
Thanks for reading and have a great week everyone,
Sav