This isn't a wind up, gather I'm a bit of a laughing stock already and only joined this site 6 hours ago Arranged with the client to install a 63A MCB after the RCD. Or is this going to cause an eruption of laughter amongst the keyboards?
 
If this is for real then please get a qualified electrician to complete the job. No offence intended but you are out of your depth I would say. Daz
 
I think you should have used 16mm² ccc=63a in that type of cable. On AEI cables it shows 47a for 10mm² ccc. If you calc 12000 /230, well I get 52a. f.l.
 
I think you should have used 16mm² ccc=63a in that type of cable. On AEI cables it shows 47a for 10mm² ccc. If you calc 12000 /230, well I get 52a. f.l.
I've been thinking about it, met with the client today and although the boiler is rated at 12kW (52.7A) it only draws 45.9A on maximum demand. I'll be calling the manufacturers helpline one Monday, as they advise 10mm H07RN-F cable is used. Which obviously isn't meeting the requirements of the CCC for the cable based on a 12kW power usage. A 50A MCB has been installed which, according to load measurements, will be suffice. I've seen on other forums that people have advised that this cable (10mm) is used for this very same boiler. A learning curve to say the least, kicking myself about the over current protection as I definitly should know that, and did. My only explanation is I'm in a job where a lot of the time I'm not doing electrical work, and so not " keepin it fresh " as they say. A couple of courses have been booked before I sit the city and guilds 2394 and 5 combined to brush up on electrical theory. Anyway, thanks to all for the helpful advice, and to the others, well, it must be great being perfect and never making a mistake
 
What is the actual voltage? 230 is the harmonize voltage but in reality it more likely to be 240 ish = 50Amps
 
What is the actual voltage? 230 is the harmonize voltage but in reality it more likely to be 240 ish = 50Amps
Actual measured voltage this morning was 236 volts. Would I be right in saying that the indicated maximum demand of an appliance is perhaps an slight over statements, to take into account other factors, such as volt drop
 

Reply to Load and heat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
913
Hello All I was hoping for some advice. We have a microwave and recently after cleaning, as soon as the microwave was plugged in, a loud humming...
Replies
3
Views
810
  • Article
Do you install new heating systems? Ever had a missing cable run between a boiler and a pump? Using MAINSLINK - the pump overrun solution - you...
Replies
0
Views
727
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock