M

mrtrump

Hi, i would like to add some extra sockets to my loft , on inspection of the existing cct installed in the loft it looks like its a radial that has been taken from the upstairs ring, spured from the back of a bedroom wall socket. I know this is not ideal but if i was to add a Fused RCD socket to the start of the cct and then added the extra sockets ( Shown in Red) would this be safe?

Any other suggestion would be appreciated?

thanks

Craigradial.jpg
 
anything after the fcu will be fused down and rcd protected (if using an rcd fcu) so although not ideal but would suffice providing vd isnt an issue
 
Sounds good to me, seen it loads of times. When all said and done all you are doing is installing a hardwired extension lead. Make sure R1/R2 and Zs are in spec though, you dont want to exceed maximum circuit length and make it dangerous. My preference would be to try and cut into the ring, and extend that.

Cheers..........Howard
 
you don't say if the ring is already RCD protected. if so, you just need a FCU to feed the radial, bearing in mind previous posts regarding load and volt drop. i would try and make connections in sockets rather than use JBs. less joins to worry about.
 
What's the layout in your loft, how are cables installed/being installed?


Thanks for the quick replys people, to answer a few of your questions..... The total floor is 4.5x4 m so the runs are not massive, so hopefully no issues with voltage drop. the cables are ran in the storage space in the eves, if that makes sense, so its easy to access.....The rest of the house is not RCD protected, but im looking into getting a new CU this year hopefully so i might just leave out the RCD FCU and stick in a normal FCU for now??

Also im unable to extend it back to the upper floor ring at the moment due to disturbing decor etc.. So i was hoping to keep it like it is but protected with a FCU..

Thanks again for your replys.
 
Thanks for the quick replys people, to answer a few of your questions..... The total floor is 4.5x4 m so the runs are not massive, so hopefully no issues with voltage drop. the cables are ran in the storage space in the eves, if that makes sense, so its easy to access.....The rest of the house is not RCD protected, but im looking into getting a new CU this year hopefully so i might just leave out the RCD FCU and stick in a normal FCU for now??

Also im unable to extend it back to the upper floor ring at the moment due to disturbing decor etc.. So i was hoping to keep it like it is but protected with a FCU..

Thanks again for your replys.

If your going to stick to the letter of the Regs then you should really fit an RCD FCU as your sockets will be for use in a domestic situation. I'm sure by not fitting that RCD FCU you will not be creating a "Death Trap" just stating that by the regs you should.

You will though have to make sure that all your disconnection times are still good as by increasing the size of the circuit will affect the Zs value, but if you fitted that RCD FCU then that would be negated. And you should also issue a MEIWC.

This may seem OTT to you but this is how it should be done and for safety reasons please think about it.
 
am i getting this post correct lads, you add a fused connection unit with rcd incorparated. is this just a 2G socket with built in rcd thyanks and sorry if im away off the mark.. im learning and im next on the list to get my first sparkie jobie
 

Reply to Loft Radial Circuit... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
637
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the...
Replies
16
Views
1K
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
620
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock