I was at an old maisonette the other day, and everything was old wiring, 3036's etc.
Then I noticed at the CU there was no apparent main earth coming from incoming supply, and it looked as though there once had been an earth clamp around the DNO supply cable,
tried Zs from cooker s/o and nothing,
Zs from sockets at 0.8, but after a kitchen unit was removed I saw an earth cable (maybe 2.5) coming out of a socket and terminating at the hot and cold water pipes...
was bonding to extraneous pipes acceptable from a cpc,
or could earths be utilized from extraneous parts,
and the sockets are all on 30a but its a radial, or at least most of seems spurred.