Discuss Max Zs value for MCCBs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi Guys,
in an installation with one main Distribution board and several submain-DBs, do when you measure Zdb on a submain-DB incomer? and do we need to verify the Zdb value with the upstream protection device?( for example, a 250A, MCCB on the MDB outgoing). If yes, how can I get the max Zs values for MCCBs ?
Thanks,
 
Yes you do need to measure it. Or in the UK you do, unsure of the regulations in the UAE, although projects I know about follow UK standards.

Zs Values can be gotten from the manufacturer. Normally have the information in pdf form on their website.
 
Yes you do need to measure it. Or in the UK you do, unsure of the regulations in the UAE, although projects I know about follow UK standards.

Zs Values can be gotten from the manufacturer. Normally have the information in pdf form on their website.
Thanks, yes we do follow BS regulations here. So I need to contact the manufacturer :thumbsup:
 
Thanks, yes we do follow BS regulations here. So I need to contact the manufacturer :thumbsup:

The max Zs is because it’s the device manufacturers specification.

I write EICR’s using the Amtech Fast test software (now known as Trimble Fast Test)
So long as you don’t have the budget version it comes with the their single line calculator.
Using single line calculator you can do the cable calls for lots of different cables and use it to obtain the max Zs for MCB’s, MCCB’s and ACB’s.

(Currently budget version is £185, version with single line calculator is £385 and expensive version is £585]
 
The max Zs is because it’s the device manufacturers specification.

I write EICR’s using the Amtech Fast test software (now known as Trimble Fast Test)
So long as you don’t have the budget version it comes with the their single line calculator.
Using single line calculator you can do the cable calls for lots of different cables and use it to obtain the max Zs for MCB’s, MCCB’s and ACB’s.

(Currently budget version is £185, version with single line calculator is £385 and expensive version is £585]
Thank you. had heard about Amtech but didn't know it has Zs values for breakers as well :thumbsup:
 
Thank you. had heard about Amtech but didn't know it has Zs values for breakers as well :thumbsup:

With the Amtech Fastest it automatically fills in BS 60898 and BS 3871 MCB’s, BS 88 fuses but not BS 60947 MCCB’s.

To get the unusual fuses, MCCB’s ACB’s you need the Amtech Single Line Calculator. If you get the budget version of Amtech Fastest, it is not included. Get the mid-cost or the expensive version. The Single Line Calculator is included free of charge.


I hope this helps
 
With the Amtech Fastest it automatically fills in BS 60898 and BS 3871 MCB’s, BS 88 fuses but not BS 60947 MCCB’s.

To get the unusual fuses, MCCB’s ACB’s you need the Amtech Single Line Calculator. If you get the budget version of Amtech Fastest, it is not included. Get the mid-cost or the expensive version. The Single Line Calculator is included free of charge.

I hope this helps
Thank you. Or probably better( cheaper) to contact more commonly used MCCB manufacturers and ask for the data.
 

Reply to Max Zs value for MCCBs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi new member here looking for a bit of advice. I recently undertook a condition report of a building where the measured Zs at the distribution...
Replies
20
Views
5K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
700
Helloo guys, First post, so sorry if this is dreary! I'll try keep it simple... I have a client with a distribution circuit supplying AC...
Replies
4
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock