Ok. I've been trying to get my head round this all day but I'm getting nowhere.

On page 45 of the OSG (Table 7.1) it says the maximum length of a lighting circuit wired in 1.5/1.0 cable on a 6 amp Type B MCB is 90 meters.

However, working out the voltage drop for this length of cable I'm getting 13.76 Volts (after correction for operating temp) which is double the allowable VD for a lighting circuit.

Am I missing something?? Does anybody know how the values in the OSG are worked out??

Any help GREATLY appreciated!!

JUD
 
the onsite guide has a specific 'Lighting' table which is what you are looking at, if you look it says "load evenly distributed" so you can't simply caluculate the voltage drop. All of the run isn't carrying the full load and so voltage drop along the circuit will differ.
Only the initial run will be carrying the full load, from there on, the load reduces as each light is fed.
 
Thanks roukel01.

After doing a bit of digging last night I came across this which supports what you have said.

the bit you are forgetting is the little comment in bold just at the top of the table...

Lighting circuits (3% voltage drop load distributed)

"Load Distributed" is the key point.

IF the whole of your 6 amps was right at the end of the 90m cable then you are correct volt drop would be 15+volts.

BUT... lets assume the load is distubuted... try a few easy numbers

Consider if the lighting circuit has 12 x 100watt light bulbs (stuff the green energy saving lark for the moment!)

AND lets say they are equally spaced along the cable run in pairs,
(could be 6 rooms each with 2 bulbs in)

so 90m length divided by 6 is 15m sections.

15m then 200w load [call this bit A]
30m then 200w load [call this bit B]
45m then 200w load [call this bit C]
60m then 200w load [call this bit D]
75m then 200w load [call this bit E]
90m then 200w load [call this bit F]


so bit F is going to carry 200w 0.87A & thus drop 0.38v (29x0.87x15)/1000.
so bit E is going to carry 400w 1.74 & thus drop 0.76v (29x1.74x15)/1000.
so bit D is going to carry 600w 2.61A & thus drop 1.13v (29x2.61x15)/1000.
so bit C is going to carry 800w 3.48A & thus drop 1.51v (29x3.48x15)/1000.
so bit B is going to carry 1000w 4.35A & thus drop 1.89v (29x4.35x15)/1000.
and
bit A is going to carry 1200w 5.22A & thus drop 2.27v (29x5.22x15)/1000.

Add all these volt drops together and you get somewhere around 7.94v

which is still bigger than the 6.9v max that you correctly mention.

But we still haven't taken account of diversity.
e.g. we have calculated EVERY light is on all the time.

if we assume the 66% diversity rule of thumb with lighting circuits
then it now drops down to approx 5.25v
Jobs a goodun as they say!!

Hope this all makes sense..

I don't know if this is how the IEE do their calcs? but they are bits that need to be taken into account.

Also don't forget... real world probably hasn't got all 100w bulbs!
chuck a few 60w / 40w, or low energy lamps in and you get numbers down to 3v 1.7%

JUD
 

Reply to Maximum Cable Length in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
832
Been out the domestic game for a long time, but now having to rewire my own house. Was wondering what the maximum cable length would be for a...
Replies
10
Views
5K
Hi guys, I'm struggling with working out the length to fill In the gaps for my upcoming exam. I'm struggling with finding the length as I don't...
Replies
1
Views
887
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
523
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock