Discuss Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

haj

-
Arms
Reaction score
47
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)
 
Always go for the better option with cable sizes. I would personally never use 16mm whatever the incomer fuse. Even if you know it's 60A or 80A, pretend it's 100A and put in 25mm2 tails ( double insulated ). The 17th Ed. recommends that anyway whatever.
 
Thanks guys i quoted OSG it says SHOULD be 25mm not must be 25mm he says leave them alone i think change them.
quite right haj, exact wording is

"polarity should be indicated by the colour of the insulation and the minimum cable size should be 25mm2"

theres 2 shoulds in that statement. would your mate ignore the first should the sameas he would the second should :eek::eek:

25mm it is then ;)
 
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)
hi i assume that it was a house you went to so has to be 25mm .also double insulated hope this helps.
 
I always use 25mm tails, just remember to upgrade the bonding cables to suit.
The meter tail size is dependant on the cutout fuse rating as far as i `am aware.
 
New posts

Reply to Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
931
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
487
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock