Discuss Motor testing in the Commercial Electrical Advice area at ElectriciansForums.net

K

Knobhead

One thing before testing a motor is check the mechanical loading. I’ve had many an argument with fitters who insist the gearbox or what ever is free.
A classic being “Jock” (fitter) insisting the Radicon gearbox was free. I was doing pull ups on a set of 18” stillsons trying to turn the motor shaft. Jock insisted it was an electrical problem, fortunately the manager showed up before we came to blows.
In a production environment you will discover everything is an electrical fault. The conveyor motor won’t run, it’s got nothing to do with the tonnes of spillage burying it.

Bearings:
If the motor is still running use a long screwdriver as a stethoscope to listen to the bearings. Place the blade of the driver on the bearing housing or the motor end bell and put your ear against the end of the handle. A rumbling noise tells you all is not well. You can try a few shots of grease, if that doesn’t quieten it down then it’s time to get the spanners out.
With the motor stopped place a bar under the shaft and see if there is any “lift” in the bearing. With roller or ball bearings you shouldn’t be able to detect any. Sleeve bearings you may get a slight amount, I’m sorry but this is one where there’s no definite answer, experience is needed with them.


Electrical tests:
I was taught to use twice the terminal voltage for IR tests but some don’t agree with this. As for minimum values I use the M&Q test method. Where leakage current should not exceed 1/10,000[SUP]th[/SUP] of the FLC. This then takes in to account that a large motor has a lot more windings than a small one and therefore a higher leakage current. With a motor that’s been in service you can’t expect to be getting infinity readings.

A motor with an internally connected star point there’s only limited tests you can do. But there again they are cheap enough to be more or less disposable.
IR test:
Due to the internal star connection you can only test the windings to earth.
CR tests:
A to B, B to C, C to A. Compare each of the three readings, they should be within a few % of each other.

View attachment 11927

A motor with six terminals whether it’s connected star of delta can be tested the same way.
IR tests:
With the links still connected test to earth. With the links in one test covers all the windings.
Remove the links and test A1 to B1, B1 to C1, C1 to A1. This checks the insulation between the individual windings.
CR tests:
A1 to A2, B1 to B2, C1 to C2. Compare each of the three readings, they should be within a few % of each other.

If the motor tests OK then it’s time to look at the starter, isolator and supply cables.
 
Last edited by a moderator:

Reply to Motor testing in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
635
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Ive had a amusing days fault finding today, Found several faults but have come out of it asking more questions than I have answers. So Me and a...
Replies
22
Views
5K
Hi Lucian. I hope you see this post that I said I was going to put up in response to your information. After what you said about being surprised...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock