Forum,

I am converting from overhead too underground service to my house. This involved moving the meter about 11 feet down a wall from its current location. The old meter base sits directly outside of the electric panel. So, at the new meter base, I plan to penetrate the exterior wall, then run service entry cable through the wall and into the basement. The service entry cable will then run under floor the joists and over to the service panel (about 11 feet).

I am thinking I am going to have a rough time getting the service entry cable to bend in such a way that I can get it into the top of the panel (where the old SE cable enters the panel). That stuff is stout!

Any advice on how to approach this problem? Some ideas that come to mind, but I am not sure of the limitations and pros and cons:

1) Rather than coming through the house at the new meter base, run the SE cable down the outside wall and into the hole where the old SE cable comes into the house and to the panel.

2) Drill holes in the one or two joists closest to the panel to get the cable above the panel. This would avoid the bend up and then back down into the panel in close quarters.

3) Bring the SE cable through the side of the panel rather than the top.

Other ideas?

Other information that might be useful:

  • The house is stucco exterior
  • Service location is in Ohio
  • The service is 200 AMP
  • The meter base includes a disconnect
  • The SE cable is Aluminum SE-U 4/0-4/0-4/0

Thanks!
Jeff (DIY)
 
Forum,

I am converting from overhead too underground service to my house. This involved moving the meter about 11 feet down a wall from its current location. The old meter base sits directly outside of the electric panel. So, at the new meter base, I plan to penetrate the exterior wall, then run service entry cable through the wall and into the basement. The service entry cable will then run under floor the joists and over to the service panel (about 11 feet).

I am thinking I am going to have a rough time getting the service entry cable to bend in such a way that I can get it into the top of the panel (where the old SE cable enters the panel). That stuff is stout!

Any advice on how to approach this problem? Some ideas that come to mind, but I am not sure of the limitations and pros and cons:

1) Rather than coming through the house at the new meter base, run the SE cable down the outside wall and into the hole where the old SE cable comes into the house and to the panel.

2) Drill holes in the one or two joists closest to the panel to get the cable above the panel. This would avoid the bend up and then back down into the panel in close quarters.

3) Bring the SE cable through the side of the panel rather than the top.

Other ideas?

Other information that might be useful:

  • The house is stucco exterior
  • Service location is in Ohio
  • The service is 200 AMP
  • The meter base includes a disconnect
  • The SE cable is Aluminum SE-U 4/0-4/0-4/0

Thanks!
Jeff (DIY)
JD buckeye if you go with copper you can drop down to 2/0 on all 3 conductors with a # 6 ground. You have to pull 4 wires from the panel to your panel inside. Question is are you an electrician. Is the a new panel - meter combo with a 100 amp breaker to feed your panel inside. It’s very important that you bond that new service to ground rods. It’s not that easy without experience and did you draw a permit. Again are you an electrician and if not you need to hire one and you can help him. Me personally I wouldn’t do it the way you are saying
[automerge]1569546717[/automerge]
Forum,

I am converting from overhead too underground service to my house. This involved moving the meter about 11 feet down a wall from its current location. The old meter base sits directly outside of the electric panel. So, at the new meter base, I plan to penetrate the exterior wall, then run service entry cable through the wall and into the basement. The service entry cable will then run under floor the joists and over to the service panel (about 11 feet).

I am thinking I am going to have a rough time getting the service entry cable to bend in such a way that I can get it into the top of the panel (where the old SE cable enters the panel). That stuff is stout!

Any advice on how to approach this problem? Some ideas that come to mind, but I am not sure of the limitations and pros and cons:

1) Rather than coming through the house at the new meter base, run the SE cable down the outside wall and into the hole where the old SE cable comes into the house and to the panel.

2) Drill holes in the one or two joists closest to the panel to get the cable above the panel. This would avoid the bend up and then back down into the panel in close quarters.

3) Bring the SE cable through the side of the panel rather than the top.

Other ideas?

Other information that might be useful:

  • The house is stucco exterior
  • Service location is in Ohio
  • The service is 200 AMP
  • The meter base includes a disconnect
  • The SE cable is Aluminum SE-U 4/0-4/0-4/0

Thanks!
Jeff (DIY)
JD I think that since you are a DIY you are way in over your head. There is so many things have to be done in the right order I cannot give you advice, the only thing you can do is hire an license electrician. Someone has to draw a permit and how are you dealing with a power company. Please this is one job you do not won’t to do own your own. Good luck
 
Last edited:
I'm commenting late at night long day.
Re DNO meter position? Are you planning to have that sited in the cellar?
If so, that's a no no these days. Classed as fire hazard and flood hazard.
 
I'm commenting late at night long day.
Re DNO meter position? Are you planning to have that sited in the cellar?
If so, that's a no no these days. Classed as fire hazard and flood hazard.
@Driver man he is just wanting to run his wire through his basement to the panel which is buy code
 
Per the advise here, I hired an electrician to help me finish the job. We penetrated the exterior wall beneath the meter base, then ran inside the basement to the panel. We entered the panel through the side and did not have to drill holes in the joists near the panel.

I really do appreciate everyone's help and advice!

Jeff
 
Per the advise here, I hired an electrician to help me finish the job. We penetrated the exterior wall beneath the meter base, then ran inside the basement to the panel. We entered the panel through the side and did not have to drill holes in the joists near the panel.

I really do appreciate everyone's help and advice!

Jeff
Congratulations Jeff and have a great day
 

Reply to Moving meter - Service Entry (SE) cable into panel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello I am trying to design an electrical service. I am a retired carpenter and trying to build a triplex for my retirement. I am hoping to get...
Replies
0
Views
736
Hi, I have a general question about main panel locations. The house is 120' long so I was contemplating running 2x 200amp panels located on the...
Replies
0
Views
806
Hi guys, I'm shadowing the electrician who is doing our EICR's and after visually inspecting the service cable and service head, I noticed a bit...
Replies
12
Views
1K
At long last my wife is getting her new kitchen and the contractor will be running 10 or so new circuits from a new sub panel. The sub panel...
Replies
1
Views
793
Short version: does code specify a minimum distance from the panel to the first grounding rod, and if so, what is that distance? Long version...
Replies
1
Views
574

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock