Hi Guys,

Contactor in plastic enclosure.

230v brown phase feeding contactor coil (230v) and neutral

230v grey phase through contacts.


Earth wires from both circuits are sleeved and the ends bent over.(no connection or terminals)
plastic din rail, no earth terminal. Would connecting these earths together cause any problem with future Insp and test? thinking of parallel paths.

no 400v sticker or isolate elsewhere or breaker id.


And no I didn't wire the circuit.

Hubsy
 
The 'brown phase' that's feeding the coil might just be brown because it's a switched live from a control point. It might be the same phase as the grey that's supplying the contacts. If you test between them when they're both live do you get 0v or 400v?

As for the earths I'd connect them together on a choc block or Wago or whatever connectors you guys use.
 
definitely 400 volts between live conductors.

Just wanted to check facts on the earth before I take it further.
regs do state that earths should be terminated, for testing.

Are the warning labels mandatory, as I believe, or are the just an extra.....
 
Just a question.
Should the grey be over sleeved with brown before/ after the contactor or both because its technically a single phase supply then.....still learnin!
.......Andy;~)
 
I personally would sleeve the cables brown if they are both on the same phase. If there are more than one phase in an enclosure, then I would sleeve them accordingly, or mark them as L1, L2 ect.
all cables on the same phase should be the same colour to avoid confusion!
 

Reply to multiple earths in enclosure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
871
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
589
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
609

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock