its seams now neutral its on the right place and not crossed any more and for that you not have any tripping..now carefully move all that circuits from RCD 1 to the original RCD you install before and see whats happened..but carefully check all neutrals if its on the right place..99% of this kind of tripping caused by cross neutrals if you understand whats mean '' cross neutral ''..Update:
I've just moved everything to RCD 1 (EXCEPT for the shower which is still on RCD 2). All seems fine now I powered up all big appliances And the shower at the same time for ab 3 mins now - no trips. Does it mean that I have reverted to my old set up where 2 RCD's have been installed and for the shower and one foe all others? How safe is this? Old CU has worked fine for the last couple of years now with all existing appliances except for the shower which I installed today hence the CU renewal...
but the best advice its what Trev says to you..