Hello everybody

Ive got my niceic inspection soon. On my recent fuse board change and test i completed Zs tests for each circuit but only calculated R1 + R2 (apart from the ring mains) IS THIS OK? Also if anyone has had the niceic guy come out, any words of warning?

Thanks
 
You MUST test R1 + R2 or R2 at every point on every circuit. This test can not be calculated.


Sent from my iPhone using Tapatalk
 
At every point on every circuit? are you sure it's not just the furthest point on every circuit?

If its a board change only
No requirement for Zs throughout the circuits,a reading at the extremity of the circuits is ok
I would also do a loop test at all the sockets if possible as well as continuity of the ring
 
i usually calculate R1+R2 on existing circuits too (except on ring circuits) and only measure it if its a new circuit. I also am looking into NICEIC enrolement soon and would like to know the assessors views on this so plz post the outcome,
cheers,
wayne
 
i usually calculate R1+R2 on existing circuits too (except on ring circuits) and only measure it if its a new circuit. I also am looking into NICEIC enrolement soon and would like to know the assessors views on this so plz post the outcome,
cheers,
wayne

If he's any good, he'll ask you what possible use a 'calculated' R1 + R2 measurement was to anyone.
 
Must admit chaps, there is no reason not to measure R1+R2 on a CU change.

This would then go towards ensuring the cpc is continuous throughout the circuit, which a Zs measurement would not.
 
Must admit chaps, there is no reason not to measure R1+R2 on a CU change.

This would then go towards ensuring the cpc is continuous throughout the circuit, which a Zs measurement would not.

I agree, Jason - measure it. Your cables are already disconnected etc etc. so why not.

A calculated R1 + R2 is as much use as a chocolate teapot - what does it tell you? Nothing.:)
 
You mention to your assessor that you calculate R1+R2 from Zs-Ze, and he'll explain why this is no good.....on your re-assessment!!
 
good post Lenny, but would be ok IMO to measure R1+R2 , and calculate Zs?
 
Last edited:
It's okay to calculate Zs based on measured Ze and measured R1+R2. But only just okay!

Measuring Zs aswell makes me feel I have completely tested the installation. Remember that Ze is measured before the CU and R1+R2 is measured after it. Measuring Zs directly at the extremities of each radial and at least one point on each ring is the only test that includes any possible poor connections, high resistance joints etc that may lurk within the board.
 
It's okay to calculate Zs based on measured Ze and measured R1+R2. But only just okay!

Measuring Zs aswell makes me feel I have completely tested the installation. Remember that Ze is measured before the CU and R1+R2 is measured after it. Measuring Zs directly at the extremities of each radial and at least one point on each ring is the only test that includes any possible poor connections, high resistance joints etc that may lurk within the board.

Agreed.

It is the only real test of a full circuit and all it's components.
 
Gentlemen

The correct method which is accepted/NIC guidance is to measure your r1 + r2 and from this you would calculate your Zs with the following equation Zs= (r1+r2)x1.2 + Ze, the reason being to verify polarity and most importantly it gives an accurate reading where your direct Zs measurement incorporates parrallel paths.

Hope this clears it.
 
Gentlemen

The correct method which is accepted/NIC guidance is to measure your r1 + r2 and from this you would calculate your Zs with the following equation Zs= (r1+r2)x1.2 + Ze, the reason being to verify polarity and most importantly it gives an accurate reading where your direct Zs measurement incorporates parrallel paths.

Hope this clears it.

The correct method?

Please post a reference for this 'correct method' I'm intrigued!
 
Gentlemen

The correct method which is accepted/NIC guidance is to measure your r1 + r2 and from this you would calculate your Zs with the following equation Zs= (r1+r2)x1.2 + Ze, the reason being to verify polarity and most importantly it gives an accurate reading where your direct Zs measurement incorporates parrallel paths.

Hope this clears it.

The correct values are R1+R2 not r1+r2, these are two very different beings.

Also a measured Zs under normal service conditions will be a more accurate reflection of the situation as the parallell paths that exist will be included as they are in normal service conditions anyway. You will also gain a truer reflection of prospective earth fault currents.



This is why for those that do it, you CANNOT calculate R1+R2 from a measured Zs reading.
 
Last edited by a moderator:

Reply to NIEIC inspection in the Australia area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
823
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock