I'm looking at a CU swap in a Flat above a shop. The MET in the Flat has no Bonding to the Gas or Water present, i think it could well be connected to the services in the shop below the flat. I know i should i run new bonding up from the property below. I've been looking...... but where in the regs do i find the exact regs relating to properties containing multiple dwellings, each with a seperate MET and connection to the Gas and water services required. Many thanks for direction on this.
 
If you don't know it, you've already answered your own question!!!

You run your bonding cables to those services in each of the multiple dwellings, from the service pipes etc that are serving that dwelling area. And you can't do any work, like change the CU, until those bonding cables are in place....

You DON'T run your bonding cables from the shop below either!!!!
 
Last edited by a moderator:
Yeah, figured that was the situation. When this property was converted to a shop below, the bonding to the services had not been added to the seperate MET for the flat above. The Gas is not a problem to locate and bring to the MET, I will have to find the Water main to the flat and bond between that and the MET.
 
Snags and Solutions - a Practical Guide to Everyday Electrical Problems: Earthing and Bonding Pt. 1: Updated to IEE Wiring Regulations 17th Edition, BS 7671: 2008 Niceic: Amazon.co.uk: Electrical Safety Council, National Inspection Council for Electr


T
hough I don't always agree with the NICEIC stance on things, one thing they do well are publications and this one above is excellent, pretty cheap at under 20 notes and in it as the scenario your facing and all the answers. Well worth getting.

And a copy of GN 8 as well
 

Reply to No Bonding to Water or Gas services in a Flat above a Shop unit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
432
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock