Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.
Discuss no continuity on ring final neutrals in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Or new skirting? - had one yesterday. Old cables (not in zones to be fair to the Chippy) so nail rignt through neutral - good shot!
Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.
Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.
if you find that it's not viable to locate the fault due to it being inaccessible without major damage, you could split the ring into 2 radials and replace the 32A MCB with 2 16A MCBs, 1 for each radial.
if you find that it's not viable to locate the fault due to it being inaccessible without major damage, you could split the ring into 2 radials and replace the 32A MCB with 2 16A MCBs, 1 for each radial.
Have you got a copy of BS7671:2008? (the book that your Periodic Inspection should be based on)I'm out.Is there a maximum number of outlets per radial though?