Good Evening all,

Been at a property today starting intial tests for a board change tommorow. There are two ring circuits, on one of the ring circuits i had an open circuit on the cpc. Live and neutral where fine 0.4/0.4. I started to locate the break by splitting the legs and joining the live and cpc going from socket to socket. After a few sockets i thought i had located the the area where the problem was as i had no continuity. However after i decided to test a few more sockets as they were close by and instead of getting an open circuit reading i got a reading of 300ohms. This throw me a little so i went back to board and checked the other ring cicuit which tested out fine 0.5/0.5/0.8. I then checked the cpc of the leg from the first ring and a leg of the different ring and got continuity which makes me think that there is a link somewhere.

It is a tncs and there is an fused spur for a pond pump which i cannot get at until tommorow due to a wardrobe in the way.

Has anyone got any suggestions for the reading of 300ohms, and other suggestions for fault finding this problem. I have taken 90% of the faces off and even though i found one slighlty loose connection it did not clear the fault.
 
good evening all,

been at a property today starting intial tests for a board change tommorow. There are two ring circuits, on one of the ring circuits i had an open circuit on the cpc. Live and neutral where fine 0.4/0.4. i started to locate the break by splitting the legs and joining the live and cpc going from socket to socket. After a few sockets i thought i had located the the area where the problem was as i had no continuity. However after i decided to test a few more sockets as they were close by and instead of getting an open circuit reading i got a reading of 300ohms. This throw me a little so i went back to board and checked the other ring cicuit which tested out fine 0.5/0.5/0.8. I then checked the cpc of the leg from the first ring and a leg of the different ring and got continuity which makes me think that there is a link somewhere.

It is a tncs and there is an fused spur for a pond pump which i cannot get at until tommorow due to a wardrobe in the way.

Has anyone got any suggestions for the reading of 300ohms, and other suggestions for fault finding this problem. I have taken 90% of the faces off and even though i found one slighlty loose connection it did not clear the fault.
wander lead (method 2) would have been better here...
 
300 ohms is probably a very long way round through items connected..... Do you have all the connections for this ring disconnected at the board?
 
disconnect the CPC from both rings....and start to narrow it down to the point where the 300 ohm continuity between em is....

it could be that when the cables were pulled in originally the holes through the joists were too small and hence overpopulated....causing the cables sheething to `burn`...and thus creating a semi conductive path between CPCs...

just a thought mind...
 
Yes all connections removed from board. But you have made me question if I had left the neutral connected at some point. Would hit be a possible explanation fo the 300 ohms
 
whats IR like?...everything clear?

if so then does every point served have R2?...
if so then do the adiabatic for time/current...

note r2 is not continuous on the cert... but that theres R2 available at each point...
 
maybe. strange things happen with neutrals.
 
you dont fail it just for the CPC not being a ring....

if you do the adiabatic...prove its good for time current (i assume its a 30-32A OPD?)...
then go round the points served...as long as R2 is there...and the adiabatic comes back OK....
then note that r2 is not continuous....
thats all really...
 
300 ohms cpc to other circuit cpc !

Multiple items on both rings left plugged in,or flexed connections still atached,cpc continuity between the rings provided by pipes between the fitted appliances

There again,maybe a slack screw or such
icon7.png
 
There might be a few things plugged in like the pond pump and a spur for an outside light which until the client moves the massive wardrobe I cannot check. ir test came in okay
 
There might be a few things plugged in like the pond pump and a spur for an outside light which until the client moves the massive wardrobe I cannot check. ir test came in okay

SO if your IR is OK then nothing is plugged in - that is if you've IR'ed all 3 cores to each other!
 
Slack screw is most common. If I get a dodgy reading first thing I do is tap all the sockets if the reading changes you've got a loosey. Tighten it up bobs your uncle. Sack off all that time consuming splitting the ring when there is no need. Other than that agree with glen get the wonder lead out.
 
Slack screw is most common. If I get a dodgy reading first thing I do is tap all the sockets if the reading changes you've got a loosey. Tighten it up bobs your uncle. Sack off all that time consuming splitting the ring when there is no need. Other than that agree with glen get the wonder lead out.
best done with an anologue instrument on an end to end....
 
you dont fail it just for the CPC not being a ring....

if you do the adiabatic...prove its good for time current (i assume its a 30-32A OPD?)...
then go round the points served...as long as R2 is there...and the adiabatic comes back OK....
then note that r2 is not continuous....
thats all really...

My issue with that solution is that there could be other more dangerous issues about to rear their ugly head. If the lack of cpc continuity is the result of a damaged cable, then their could potentially be sheathing or insulation damage.
Personally, I'd want to find out.
 
Best way and clearest way to pinpoint the problem would be to firstly liven up the ring affected only and note which sockets are live. Then disconnect one of the legs at the board and split the cables at each socket. Liven up the ring and go socket by socket with a voltage indicator between line and earth. Connect each socket back one by one until you reach the leg that fails to give you 230v between line and cpc. The leg that fails to give you this is the fly in the ointment job done!!
Just hope the one down isn't a pig to rewire or repair!!
 

Reply to no cpc continuity on ring final, strange readings ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
269
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
448
I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on...
Replies
86
Views
6K
Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
440

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock