Good Evening all,
Been at a property today starting intial tests for a board change tommorow. There are two ring circuits, on one of the ring circuits i had an open circuit on the cpc. Live and neutral where fine 0.4/0.4. I started to locate the break by splitting the legs and joining the live and cpc going from socket to socket. After a few sockets i thought i had located the the area where the problem was as i had no continuity. However after i decided to test a few more sockets as they were close by and instead of getting an open circuit reading i got a reading of 300ohms. This throw me a little so i went back to board and checked the other ring cicuit which tested out fine 0.5/0.5/0.8. I then checked the cpc of the leg from the first ring and a leg of the different ring and got continuity which makes me think that there is a link somewhere.
It is a tncs and there is an fused spur for a pond pump which i cannot get at until tommorow due to a wardrobe in the way.
Has anyone got any suggestions for the reading of 300ohms, and other suggestions for fault finding this problem. I have taken 90% of the faces off and even though i found one slighlty loose connection it did not clear the fault.