Slack screw is most common. If I get a dodgy reading first thing I do is tap all the sockets if the reading changes you've got a loosey. Tighten it up bobs your uncle. Sack off all that time consuming splitting the ring when there is no need. Other than that agree with glen get the wonder lead out.
best done with an anologue instrument on an end to end....
 
you dont fail it just for the CPC not being a ring....

if you do the adiabatic...prove its good for time current (i assume its a 30-32A OPD?)...
then go round the points served...as long as R2 is there...and the adiabatic comes back OK....
then note that r2 is not continuous....
thats all really...

My issue with that solution is that there could be other more dangerous issues about to rear their ugly head. If the lack of cpc continuity is the result of a damaged cable, then their could potentially be sheathing or insulation damage.
Personally, I'd want to find out.
 
My issue with that solution is that there could be other more dangerous issues about to rear their ugly head. If the lack of cpc continuity is the result of a damaged cable, then their could potentially be sheathing or insulation damage.
Personally, I'd want to find out.
hence my posts at #4, #8 & #11
 
Best way and clearest way to pinpoint the problem would be to firstly liven up the ring affected only and note which sockets are live. Then disconnect one of the legs at the board and split the cables at each socket. Liven up the ring and go socket by socket with a voltage indicator between line and earth. Connect each socket back one by one until you reach the leg that fails to give you 230v between line and cpc. The leg that fails to give you this is the fly in the ointment job done!!
Just hope the one down isn't a pig to rewire or repair!!
 
Evening all,

Thank you for all your advice recently. I eventually tracked down the a broken cpc in a junction box which was broken where the cable came into the jb not at the terminal. There where also a few loose connections on some old face plates.

Cheers all, just about start my next thread as i need some more advice
 
I'm glad the OP has found and fixed his fault, which luckily doesn't sound like it needed the house torn apart to access.

But I don't agree with this at all:

Best way and clearest way to pinpoint the problem would be to firstly liven up the ring affected only... until you reach the leg that fails to give you 230v between line and cpc

The OP says his 'break' measures 300 ohms. A voltage indicator will see straight through that and continue to show voltage beyond the fault. If, on the other hand, the fault does go open circuit, connecting the indicator beyond it will raise the disconnected section of CPC and any associated metalwork to an elevated voltage, and one is then relying on the test current being limited to avoid creating a shock hazard.

My point is this (and it's a point I've made before) Why use a potentially unreliable live test when the fault has been effectively shown up by a dead test? Why would you not continue tracing with an ohmmeter?
 