JimmyDaWolf

I've just been to a customer who has had somebody else carry out an EICR and have told them that it can not be passed as satisfactory until they replace a number of MCB's for RCBO's as there is a new law that requires them. This is not just on socket outlets. They have gone all out on cables concealed in walls less that 50mm etc.

Have i missed out on something here or are they just try to have there pants down. An EICR can be passed satisfactory with C3 recomendations for improvement. This was installed in accordance to it regulations at that time and thats what should be taken into consideration by the tester. Sometimes things like this make you question yourself but i think this is BS.
 
Last edited by a moderator:
Sounds like the usual scaremongering that does unfortunately go on. Maybe worth a call to the person who carried out the EICR to find out exactly why they have coded it like it is.
 
Its coded a C3. Which is pretty standard if you ask me. I'd always recomend rcbo's. Especially on socket outlets. I would deem the installation unsafe and unfit for purpose because of it tho. They have put a quote exceeding £5,000.00 to bring it up to current standards and to pass it off.
 
If its coded C3 then that doesnt make the install unsatisfactory. Only C1 and C2 give it that status.
 
No, but dont forget the report is the opinion of the person carrying it out. Although sometimes yes you see things that make you wonder why!!!
 
Its coded a C3. Which is pretty standard if you ask me. I'd always recomend rcbo's. Especially on socket outlets. I would deem the installation unsafe and unfit for purpose because of it tho. They have put a quote exceeding £5,000.00 to bring it up to current standards and to pass it off.

I think this says it all.
 
  • Like
Reactions: 1 person
License to print money. ha ha
 
I think i'll produce them now with a letter quoting a few regs and definitions. I personally prefer to look after my customers rather than fleece them. I always make it clear that they have no obligation to use us for the rectification work should there be any. I find it goes a long way to work with people rather than against them. This company have 40 properties in the U.K. sometimes people should take a step back and look at the bigger picture
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Very simple.

If the customer has email them, I suggest that you send the Electrical Safety Council - Best Practice Guide No 4 - which is a useful guide for sparks, homeowners & landlords
 
They have put a quote exceeding £5,000.00 to bring it up to current standards and to pass it off.

Sounds about right, good pricing that..lol
 
Its to replace about 60 mcbs for rcbos

I take it then that the property is commercial or industrial. 60 breakers is a lot for a house :)
 
What is the building?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
No RCBO's = Unsatisfactory
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
JimmyDaWolf,
Last reply from
Spoon,
Replies
18
Views
2,504

Advert