EICR, Tns supply, 60A fuse. 16mm tails, Main earth 10mm, gas & water bonds 6mm. Code 2?
Guess it's the fact that the supplier's earth to the MET is only 10mm that's making me feel the Code 2 is harsh!
 
Last edited:
can't see any reason for a code at all.

I'm fairly new to this side of things, but shoving my face in whenever possible to try and learn. My thoughts are a 16mm cable will carry 87A clipped direct which is more than enough for the 60A fuse. Table 54.7 says that a 16mm line conductor needs a 16mm protective conductor, but it's also possible to calculate the required size (but since we don't know the prospective fault current I can't have a pop at working this out). Then looking at 544.1.1 for the main bonding, this states that 6mm is fine where not PME conditions.

So assuming the adiabatic checks out, I'm with Tel - what is the reason for any code?

(P.S. If I've gone wrong somewhere, happy to be corrected :) )
 
Last edited by a moderator:
Yikes, I'm glad I asked! I've completely "mis-remembered" Reg 544.1.1. As you have all said, no reason for any Code. Adiabatic calls for 6mm (first standard size for unprotected conductor) so the 10/6mm are fine.
I must spend more time re-reading the Big Yellow:dunce2:
 
one has to try these days. getting cynical in my old age.
 
I'm fairly new to this side of things, but shoving my face in whenever possible to try and learn. My thoughts are a 16mm cable will carry 87A clipped direct which is more than enough for the 60A fuse. Table 54.7 says that a 16mm line conductor needs a 16mm protective conductor, but it's also possible to calculate the required size (but since we don't know the prospective fault current I can't have a pop at working this out). Then looking at 544.1.1 for the main bonding, this states that 6mm is fine where not PME conditions.

So assuming the adiabatic checks out, I'm with Tel - what is the reason for any code?

(P.S. If I've gone wrong somewhere, happy to be corrected :) )

Don't need to know the PFC to conduct the adiabatic equation.
Just use the tabulated values in BS7671.
 

Reply to Not sure why I'm asking, but..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
852
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock