Discuss prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
B
benpollard
on electrical installation certificate at the top under supply characteristics it asks for
(next to single phase) a prospective fault current in KA
How do i measure this reading please?
Thanks!
It's the highest reading between your PSCC & PEFC.
Sent from my iPhone using Tapatalk.
Test between line and neutral (PSCC)and then line and earth (PEFC)and record the highest measurement with your meter on the correct setting.
If TNCS both should be the same.
PFC. Hi. ( you don't use no-trip for Ze and pfc at origin.). with your main switch OFF. and main earth disconnected from MET. remember this is a live test . the other way is to enquire the value os Ze ( good luck with your interminable lengthy phone calls ) and calculate the pfc.
my error, there . well spotted IQ. a bit slow today, got man flu, and a deficiency of alcohol.
Reply to prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...