Steveb555

Industrial installation (non-domestic). Here's the scenario:

A large (150kW) 3-phase motor circuit where the supply is taken from a starter fitted with 315A BS88 HRC fuses.
From calculation using the cable data, the Zs value exceeds the manufacturers requirement for 5s disconnection time (similar to table 41.4 of the 17th Edition).
An additional earth cable has been installed to a main earth tape located near the motor end to achieve supplementary bonding.

My questions are: 1). How can this addition of supplementary bonding prove compliance with the regs? and 2). What use is an earth loop impedance test taken at the starter?

Any comments gratefully received.

Thanks in advance. Steveb555
 
What your doing by your supplementary equipotential bonding is trying to limit the touch voltages to 50v, so therefore if you have a high Zs by bonding your applying additional protection.

Where and what are you bonding. You can only bond an extraneous conductive part, so therefore sticking a load of G/Y cables to say a motor frame will not do al ot if it is not either an exposed/extraneous conductive part. You can check if this metal is earthy by doing the test as in 415.2.2

I'm not sure what you mean by your other point sorry.
 
Thanks for your response Malcolm. Much appreciated.
I can see your point of limiting the touch voltage so presume this should be tested as part of the regular inspections for installations which can't satisfy the 5s disconnection time by the Zs value?

My other point was just a question about the validity of the results from performing an earth loop impedance test because the result would not be influenced by any supplementary bonding at the motor end.
 

Reply to Question regarding high Zs on 3-phase motor circuit using BS88 fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K
Hello everyone, I have my AM2 fault finding resit on Friday and just wondering if anyone has any top tips as I don’t get to do any fault finding...
Replies
1
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock