I have a couple of questions regarding PV systems if anyone can help

1) Thinking of Ohms law, how does a grid tie inverter match the mains grid power

set up 2.76Kwp system of 12 panels at 230w

e.g. - Vmp 29.9 Imp 7.69

in 1 string it would mean a system Vmp of 358.8 V and IMP of 7.69, but the inverter outputs at 230v

does this mean the inverter increases the amps in order to drop the voltage ( i know we loose some due to inverter inefficiency aorund 10% or does the inverter increase the amps so that it balances )
or is the remaining voltage lost in heat (resistance)

or if we have the setup in 2 string with a system IMP of 15.38 and Vmp of 179.6

in this instance does the inverter vary the amps in order to increase the voltage to 230v ?

or again is some of the amps lost in heat (resistance)

i know a bit about PV but this has raised some interesting questions - my assumption is (knowing how hot invereters get ) that wwe loose the excess in heat

2) other than limiting the voltage to more managable levels and increasing shading tolerances what are the advantages of increasing the number of strings
 
Panel amps/voltage bear no relationship in terms of what comes out of the inverter. Panels generate dc, invertor converts it to ac. Only thing that links them is power out is slightly less than power in.
 

Reply to Questions Regarding Strings in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
839
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Good Evening All, I'm not an electrician but I'd like to pick the brains of those that are please. Note I intend getting a qualified electrician...
Replies
0
Views
1K
Hi there, I just purchased a sailboat and its electrical system was put together in questionable ways.. It came with an 815W array of mismatched...
Replies
4
Views
2K
I'm relocating a 16 panel system from a field onto a barn roof. Currently, there are 16 panels, wired as two strings into an isolator. From the...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock