Hi All, quick question before bed.
Just come back from an emergency callout
Full installation isolated - customer re-energized when I walked out of the door due to medical conditions
Thoughts please with particular attention to point 2! - will pick this up in the morning
Just come back from an emergency callout
- No Earth in property
- 6 double sockets on a 15A Radial (over 2 floors)
- 3036 CU with big hole out of R/H side
- Bonding to mains Water - 16ohms through this means
- No Bonding to Gas
- Pre RCD covering 4 x 3036 CUs
- Pe-RCD not holding on circuit 6 (point 2) - all appliances are class 2
- All IRs are >150Mohms
Full installation isolated - customer re-energized when I walked out of the door due to medical conditions
Thoughts please with particular attention to point 2! - will pick this up in the morning