hey all
i was wondering what reason would be behind an RCBO tripping out before the ramp test has finished and comping up with trp?
thanks
Not sure what you mean with"before the ramp test is finished". The whole purpose of the ramp test is to find out what current will cause the device to operate, when your meter comes up with trp it should have some more info on there for you.
what i mean is when i drop my test leads on the rcbo and press test. the rcbo will then trip out and the meter will say trp on the screen giving no result. the tester its a megger mft1552
ive changed the rcbo as well
all other rcbo's trip within in limits
You are getting confused here with X.5 / X1 / X5 test and ramp testing you shouldn't need to ramp test a rcd unless you are trying to resolve tripping issues.
i am trying to resove tripping issues
So there's nuisance tripping on one RCBO?
What happens on the half test? If it's tripping immediately on a ramp I'd expect it to be but as Murdoch said have you made sure that all loads are removed and the IR is ok?
i have and the reading was appauling between n and e, also all 27 lights have their own joint boxes burried under a garden spanning over 100 meters.
to add to the last reply between neutral and grey (spare core), which will be used as a live is also down, which has nothing connected to it as of yet
probably tripping due to fault on circuit and 1552 is aborting test.
Leave the garden lighting circuit off (physically disconnected)for a week if it stops tripping then probably water ingress in the fittings or joint.
well thats what i thought, but i sealed them pretty well in galv boxes covered in magic gel, been ok since christmas and had a lot of rain in that time
So this immediate tripping on a ramp is after you have disconnected the circuit completely? Also the cables are failing their IR?
You have a couple of problems in this scenario.
Reply to rcbo tripping before ramp test is complete in the UK Electrical Forum area at ElectriciansForums.net
Folks. I need to install a defib unit outside on a wall. Does this require an RCBO or not, just wondering as the unit has a small heater within...
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...