I would say the special location is the whole bathroom. The different zones indicate the ip rated equipment that can be used in a particular zone. Whole bathroom I.e. Special location, all circuits need RCD protection. That's how I determine it
 
Beat me to it
but when you lot go independent and we build a big trench right through the Watford gap then it will be to late to rape and pillage in England Archie
 
here is one. the DB has a rcd covering all circuits but the lighting circuits. the bathroom is classed as a special zone so the lighting in the bathroom needs to be rcd protected "lighting in zone 2,3". what are your thoughts on putting an rcd spur outside the bathroom next to the fan isolator for example?
 
here is one. the DB has a rcd covering all circuits but the lighting circuits. the bathroom is classed as a special zone so the lighting in the bathroom needs to be rcd protected "lighting in zone 2,3". what are your thoughts on putting an rcd spur outside the bathroom next to the fan isolator for example?

I think it will look quite pretty next to the fan isolator. Are you connecting anything into it ? If so, what are your thoughts on this with reference to compliance with the regulations ?
 
i did this with ip65 downlights in a home that did not have any rcd's "old re-wireables " i did a post a while back on here. tbh i hope one day rcbo's become really cheap so we could just have every circuit on its own. saves half or all circuits going off at one time XD

reading threw a document from a site it says

Zone 0 is inside the bath or shower itself. Any fitting used in this zone must be low voltage, (max 12v) and be rated at least IP67 which is total immersion proof.
Zone 1 is the area above the bath to a height of 2.25m from the floor. In this zone a
minimum rating of IP44 is required. If the fitting is 240v a 30ma residual current device
(RCD) must also be used to protect the circuit in this zone.
Zone 2 is an area stretching 0.6m outside the perimeter of the bath and to a height of
2.25m from the floor. In this zone an IP rating of at least IP44 is required. In addition it
is good practice to consider the area around a wash basin, within a 60cm radius of any
tap to be
considered as zone 2.
Zone 3 is anywhere outside zones 0,1 and 2 (subject to specific limits) and where no
water jet is likely to be used. No IP rating is required. In addition to the above, if there is
a likelihood of water jets being used for cleaning purpose in zones 1,2 and 3 a fitting
rated a minimum IP65 must be used
 
i did this with ip65 downlights in a home that did not have any rcd's "old re-wireables " i did a post a while back on here. tbh i hope one day rcbo's become really cheap so we could just have every circuit on its own. saves half or all circuits going off at one time XD

reading threw a document from a site it says

Zone 0 is inside the bath or shower itself. Any fitting used in this zone must be low voltage, (max 12v) and be rated at least IP67 which is total immersion proof.
Zone 1 is the area above the bath to a height of 2.25m from the floor. In this zone a
minimum rating of IP44 is required. If the fitting is 240v a 30ma residual current device
(RCD) must also be used to protect the circuit in this zone.
Zone 2 is an area stretching 0.6m outside the perimeter of the bath and to a height of
2.25m from the floor. In this zone an IP rating of at least IP44 is required. In addition it
is good practice to consider the area around a wash basin, within a 60cm radius of any
tap to be
considered as zone 2.
Zone 3 is anywhere outside zones 0,1 and 2 (subject to specific limits) and where no
water jet is likely to be used. No IP rating is required. In addition to the above, if there is
a likelihood of water jets being used for cleaning purpose in zones 1,2 and 3 a fitting
rated a minimum IP65 must be used


must be an old doc. zone 3 is no more. it is an ex-zone. stuck to it's perch with glue.

 
i did this with ip65 downlights in a home that did not have any rcd's "old re-wireables " i did a post a while back on here. tbh i hope one day rcbo's become really cheap so we could just have every circuit on its own. saves half or all circuits going off at one time XD

reading threw a document from a site it says

Zone 0 is inside the bath or shower itself. Any fitting used in this zone must be low voltage, (max 12v) and be rated at least IP67 which is total immersion proof.
Zone 1 is the area above the bath to a height of 2.25m from the floor. In this zone a
minimum rating of IP44 is required. If the fitting is 240v a 30ma residual current device
(RCD) must also be used to protect the circuit in this zone.
Zone 2 is an area stretching 0.6m outside the perimeter of the bath and to a height of
2.25m from the floor. In this zone an IP rating of at least IP44 is required. In addition it
is good practice to consider the area around a wash basin, within a 60cm radius of any
tap to be
considered as zone 2.
Zone 3 is anywhere outside zones 0,1 and 2 (subject to specific limits) and where no
water jet is likely to be used. No IP rating is required. In addition to the above, if there is
a likelihood of water jets being used for cleaning purpose in zones 1,2 and 3 a fitting
rated a minimum IP65 must be used

Why are you reading some out of date info from a website ? All the relevant info on this matter is in your regs book ......
 

Reply to RCD on bathroom lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
980
Hi all, I'm wondering if it's permitted to replace an outside wall light myself if I use the existing wiring from the old light. In theory I just...
Replies
2
Views
613
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock