Hi wondering if some1 can advise me on a job I have been doin I've run a 10mm swa 3core to a outer building office mostly buried into a consumer unit protected by a rcd . At the house end consumer is it best to terminate in rcd side of board? or general supply side ?... Because if I terminate in rcd side if a fault was to occur in outer building it would interfere with power in house or do I place a separate rcd next to house consumer ?
 
the SWA does not require RCD protection. RCD is best fitted at the outside building. the only time you need RCD at the front end is if there's T/E buried in walls in the house before joining to SWA.
 
Thanks no nothing buried at house end just exits board into plastic adaptable box then swa out to outer office which is 30m away
 
then feed from a non-RCD way in the house CU. fit RCD/s in office.
 
Why do you want to create a situation where you would not have any discrimination between the two RCD's?? Supply the outbuildings SWA cable from the unprotected side of the main consumer unit!!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Rcd protection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
dal_87,
Last reply from
MDJ,
Replies
5
Views
1,385

Advert