Discuss RCD refuses to switch on (up) in the Electrical Forum area at ElectriciansForums.net
J
John Chalmers
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
Aico 3000
Wetroom Store - Network Wetroom Suppliers
Midwest
Midwest
Firstly I hope you know what you are doing and can carry out safe isolation?
Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
Pete999
Pete999
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.
J
John Chalmers
  • #5
I worked for years in electrical wholesalers and understand matters fine.
I reckon I do have a fault, however I cannot understand where. I tripped the in-house mcb and then disconnected the RCD, now when switched up it stays up.
Surely this means the fault is between the cu and the RCD, as I have thought until now, it’s simply a single length of cable within plastic conduit, even through the wall and right into the RCD! Thanks.
buzzlightyear
buzzlightyear
I had a customer did what the op tried to do ,he came of worse in the end .
J
John Chalmers
  • #7
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
Pete999
Pete999
Sorry misunderstood your description, my error
Pete999
Pete999
What you describe as an ELCB what make and type is it
Scolmore Electrical Products
Reply to RCD refuses to switch on (up) in the Electrical Forum area at ElectriciansForums.net
CK Tools :) The professionals choice when it comes to Electrical Tools
Top Bottom