Discuss RCD tripping times, 0.4 or <200 etc..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I always been told that an 30m/A RCD should trip within 200m/s (x1) and 40m/s (x5). But something iv never taken much notice of before is on test sheet the maximum disconnection time of a circuit less than 32A is 0.4. So....which is it? within 0.4 or within 200m/s????
0.4s = 400ms for TN disconnection times<= In 32A, and 5s for >32A In or distribution circuits.
for TT 0.2s and 1s respectively
An RCD/RBO is faster in both cases, 40ms (@5XIdn) = 0.04s
So the max disconnection time for a circuit <32A is 400m/s. Yet the RCD has to trip <300m/s? Are you saying an MCB's max d/connection time is <400m/s? If so there is no way to test the tripping time of an MCB as far as i know? :S
Circuits supplied by a TN system, as it stands at present, should be designed to disconnect in 0.4sec. It is a comparatively modern idea to use RCDs/RCBOs on all circuits (Its very European you know !)
See 411.3.2
RCDs are used to provide additional protection, but can also be used as fault protection where the normal method is for some reason insufficient to give a disconnection time less than Table 41.1.
If the RCD is for 30mA or less, and used for additional protection, then this is tested @ 5X Idn and should trip in less than 40ms, (I have missed out the 1/2 Idn,1X Idn and 0 and 180 degrees etc. for clarity), all other RCD's (100mA etc.. used for dist. circuits) are only tested at 1/2 and Idn, does this help ?
30mA or less RCD's are for additional protection of final circuits.
Actually one more question. How can you test that a circuit disconnects in <400ms (0.4) if it has no RCD on it?​
By calculation (max Zs etc.) and the tripping curves in the BGB, you have to just take this at face value, as we lowly sparks do not have the equipment to test this.
Lets say iv got a circuit. Its TNCS and its on a 10A MCB and has a 63A, 30m/A RCD covering it. If i do an RCD test its should trip out in <300m/s yes?
It will depend what the current flow is at the time of disconnection.
To meet the requirements of BS 7671 it must trip out at <=300ms at its IAN, and 40ms at 5 times its IAN
An earth fault current of minimal impedance covered by a 10A MCB will disconnect as fast as an RCD, probably quicker. Some manufacturers have data sheets showing a likely disconnection of 0.01s.
quick question as well re RCDs, testing a village hall with 30ma up front of everthing rcd trips on 1/2 test With message TRP on the tester fine at x1 28 ms, same as 1/2 on x5 trips with TRP message, checked the booklet with the tester says that message is leekage on the curcuit, but its the same for all 16 curcuits, TT system 194 oms RA sound like a faultly trip ? All insulation test are >500 .
You should be testing at the load terminals of the RCD with the circuit/load cables disconnected. You won't see any natural leakage then... What do you expect with 16 circuits being monitored??
I would do a ramp test and see what value it is actually tripping at with everything disconnected, it could be that on a single up front RCD that you have too much (normal) leakage, which is pushing it over the edge at 1/2Idn, and of course as you know, it should not trip at 1/2Idn.
The ramp test came in at 18ms with all curcuits/loads which can effect readings off.
Reply to RCD tripping times, 0.4 or <200 etc..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
So to start off with i’ll tell you i’m a young electrician, 23, I am qualified but obviously will always be learning. Was carrying out an eicr...
Hi Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring...
4K
Hi I'm removing an extractor fan from our WC, as it's just a toilet and sink and we never use hot water in there anyway... The extractor is on...
4K