Discuss recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
P
pepparz
on a schedule of circuit details for a installation certificate, under the circuit conductors cpc size in mm², what should be recorded when a SWA cable has been used but one of the inner conductors is used as the cpc (say single phase circuit supplied by 2.5mm² 3 core, 1 x phase, 1 x neutral, 1 x earth). should the cpc be recorded as the armouring or the 2.5mm² designated cpc conductor?
I personally think it should be the 2.5mm² designated conductor and not the armouring, which is the earth by default.
agree with that, as the armour is not always used as cpc, although it must be earthed.
On a two core you would declare the armour as the CPC size. If using a 3rd core and the armour both as your CPC, would you not aggregate the two sizes?
If you are just earthing the armour at one end then just the core size would be the CPC
but when would you design and install a circuit which needed both the armoring and a inner core to be the cpc. surely the cable should comply with just the inner core been the cpc?
it must comply if the cpc core is the same size as the line conductor. the point is that on your sotr, there's just room in the box to enter the core size e.g.2.5. where in hell are you going to fit "22mm steel armour having an equivalent copper size of 3mm"?
ive got the schedules of about 20 DB's and the cpc size has been entered as "ARM"
I would say that would be OK for a two core cable without a core used as the cpc, if there is a core as the cpc then that is the size of the cpc, though I suppose you could say 2.5+armour, but this would not be totally according to the regs as you cannot use a combined mix of materials and sizes to meet the cpc requirements.
...... you could say 2.5+armour, but this would not be totally according to the regs as you cannot use a combined mix of materials and sizes to meet the cpc requirements.
I always believed the regs did allow this, certainly the mix of cable & sheath (armour) to meet the CPC is my interpretation of 543.2. And by default Ive always assumed that this (copper & steel) allows different materials/sizes to be used unless there is another reg I've overlooked?
New posts
Reply to recorded cpc size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...