Discuss Refurbishment. Help needed with spooky ancient meters. in the UK Electrical Forum area at ElectriciansForums.net

The cast-iron head is due for replacement. There is a significant risk of personal injury if anything goes wrong there, so it should not be disturbed by anyone not wearing arc-flash protective clothing (and it is also in theory an offence to interfere with the DNO's equipment unless authorised.) As your spark mentioned, the live terminals at the bottom are connected to the public supply, if they are shorted out it will be the entire street or neighbourhood that goes black and molten metal will be sprayed in the face of whoever does the shorting. It should all be enclosed and sealed, and these days preferably replaced with an all-plastic unit. Advise the DNO and they will probably be quite happy to upgrade.

The meters do not look very spooky to me, just ordinary meters. One is presumably redundant, the other ought to be metering the supply to the house but evidently isn't. There's nothing mystical, the speed of rotation should be exactly proportional to the load; two 2kW heaters should make it go twice as fast as one, and with the main switch off it should stop completely. If it does not, then either it is faulty in some peculiar way, or it is powering something you don't know about and registering the usage accordingly. In the first case, it is the Energy Supplier's problem to rectify, or they will send their appointed Meter Operator to do it. I have no idea of the liabilities involved if the estimated account is far adrift from the meter reading. If the meter is registering a legitimate load (such as a heater running in a shed that has been on for years) then it might get a bit more tricky as the customer will be relying on their clemency to cancel some or all of the bill. If they have been lax in checking the meter or requesting customer readings, there might be hope.

How large might the bill be? You say 26 seconds per revolution. A meter of that type might typically make 150 revs/kWh. Take the current price of electricity as 14p/kWh.
3600/(26 x 150)= 0.92kW
0.92 x 0.14 x 24 x 365 = £1128 per year (if 150 rev/kWh meter)
But, if the recording train is not turning and registering on the dials, then it might be zero. All a bit vague so you'll have to bite the bullet. Might be worth checking the reading as it stands, with the estimate on the bill, to get an idea of what to say.

And, for the record, this is an old and spooky electricity meter. Actually, not spooky either, just a very clever piece of engineering from about 120 years ago that is still working perfectly today.

Aron meter 1.jpg
DSCF2032.JPG
DSCF6145.JPG
 
Yes it's a plumb bob, the meter is most accurate when correctly upright. I won't clutter this thread with more chat about the Aron meter. I'd point you at its page on my website but that is offline today for no obvious reason (it was working yesterday.)
 
I did have it running on the sideboard too. It's a bit obtrusive, two clocks ticking away, a clunk every 30 seconds as it winds the mainspring, and the suspense of waiting for the little click every 15 minutes that heralds the reversal of coil polarities and clock rates.
 
well today we had your machine in mind when we explained to the lady about the probable fault in the meter. she doesn't want to change the meter. (I think it is wise to keep the one she has) but one of our team today mentioned that the meter has two coils. is it possible that one coil is damaged which is causing the dials to not advance? She asked our electrician if the supplier would change the meter to an old Landis Gyr one. But what are the chances of that?
 
The supplier will fit whatever type of meter they prefer, you don't get to choose which manufacturer or model of meter you get.
The are all approved to the same standard and class of accuracy which is legally required for use in billing.
 
The cast-iron head is due for replacement. There is a significant risk of personal injury if anything goes wrong there, so it should not be disturbed by anyone not wearing arc-flash protective clothing (and it is also in theory an offence to interfere with the DNO's equipment unless authorised.)
For the benefit of the OP, here is an example of what can go wrong with professionals working on a live supply, and the benefits of proper arc-flash PPE that allow a sporting chance of escaping with little injury (but probably browned trousers):

View: https://www.youtube.com/watch?v=Z3yKFLJpnhI
 

Reply to Refurbishment. Help needed with spooky ancient meters. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
349
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock