HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
Evening..

I have a seperate oven and hob to fit.

The oven is 2.6kW, the hob is 3kW. I have fitted 4mm flex to the oven and the hob comes prewired with 2.5mm.

Zs on the cooker circuit is 0.2Ω making the PFC 1150A.

I was planning on connecting both to a dual cooker outlet plate fed by a 32A MCB (as reg 433.3.1(ii) shows that I can omit over current protection). However reg 433.3.1(ii) also states that it must be protected against fault current (hence reg 434.5.2).

In this example
t=0.1s
K=115
S=2.5mm
I=1150A

meaning that K²S² < I²t so the 2.5mm conductor may breach its permitted limiting temperature during a fault.

A couple of questions:

1. It would be common to have a 2.5mm radial circuit on a 20A MCB (I could even reduce the MCB on the above circuit to 20A) but if the Zs was 0.2Ω as above it would still not have adequate fault protection as K²S² < I²t??

2. If the Zs was higher (anything over 0.26Ω in the above example) then K²S² > I²t and the 2.5mm would not breach it limiting temperature in case of a fault, so it seems better to have a higher resistance!! Which doesn't make sense?
 
Last edited:
You have taken your time as 0.1s however at 1150A the circuit breaker will trip in about 0.01s (according to most manufacturers time current curves)
If you were taking 0.1 s you should then choose the lowest current that can cause this disconnection time, 160A and be aware of the current limiting characteristics of the MCB so that you can take account of the actual higher current that may flow, because then only about 750A would flow and alter your calculation again..
However remember that the prospective fault current is just that, prospective and so will not be reached in most cases of an actual fault.

Ideally you would use tabulated values of the I²t for the MCB as this will give you the correct result.

I have not done this but I am sure that the cable would be protected. (*ready to be proved wrong!)
 
You have taken your time as 0.1s however at 1150A the circuit breaker will trip in about 0.01s (according to most manufacturers time current curves)
If you were taking 0.1 s you should then choose the lowest current that can cause this disconnection time, 160A and be aware of the current limiting characteristics of the MCB so that you can take account of the actual higher current that may flow, because then only about 750A would flow and alter your calculation again..
However remember that the prospective fault current is just that, prospective and so will not be reached in most cases of an actual fault.

Ideally you would use tabulated values of the I²t for the MCB as this will give you the correct result.

I have not done this but I am sure that the cable would be protected. (*ready to be proved wrong!)

Thankyou Richard,

That all makes perfect sense. It always seems obvious when its explained well! Why would I think to use 1150A when the tables clearly show 160A for a disconnection time of 0.1s!
 
Ze = 0.17Ω. Guess the bonding must be pretty good! Any ideas on the question?

Ze test should not include the bonding, you are verifying the impedance of the means of earthing, extraneous conductive parts are not generally permitted as a means of earthing so should be excluded from the test.....PSCC/PEFC should include the bonding as parallel paths may reduce the impedance of the actual fault path and increase PSCC/PEFC.
 
Ze test should not include the bonding, you are verifying the impedance of the means of earthing, extraneous conductive parts are not generally permitted as a means of earthing so should be excluded from the test.....PSCC/PEFC should include the bonding as parallel paths may reduce the impedance of the actual fault path and increase PSCC/PEFC.

Surely it only affects PEFC and not PSCC.
 
Ze test should not include the bonding, you are verifying the impedance of the means of earthing, extraneous conductive parts are not generally permitted as a means of earthing so should be excluded from the test.....PSCC/PEFC should include the bonding as parallel paths may reduce the impedance of the actual fault path and increase PSCC/PEFC.

I realise that Wirepuller, although my post was probably not clear enough! Zs = 0.2 and Ze = 0.17. I doubt the R1+R2 of the cooker circuit is 0.03, so I made a bit of a shot in the dark at the bonding being the reason!
 
Depends on earthing type, would affect the PSCC on a TNCS/PME system.

Well with all earthing systems the neutral is earthed (otherwise it wouldn't be neutral), but point taken that with TN-C-S it may have a more severe effect on it.
 

Reply to Regulation 434.5.2 exceeding limiting temperature of conductor. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Second post on an EICR I did today (always a good sign!) 70s flat with earthed conduit and singles. 6mm runs from the CU to presumably where an...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock