Ze test should not include the bonding, you are verifying the impedance of the means of earthing, extraneous conductive parts are not generally permitted as a means of earthing so should be excluded from the test.....PSCC/PEFC should include the bonding as parallel paths may reduce the impedance of the actual fault path and increase PSCC/PEFC.
I realise that Wirepuller, although my post was probably not clear enough! Zs = 0.2 and Ze = 0.17. I doubt the R1+R2 of the cooker circuit is 0.03, so I made a bit of a shot in the dark at the bonding being the reason!