The only problem with checking End to ends at a socket (which I often do), is that you leave any paralell paths in circuit, I.e. I have had it before where you get cpc-cpc continuity at a socket but not at the board, turned out to be an undersink water heater. For that reason I always do at least and cpc end to end at the fuseboard