Hi all
I have 2 quick questions regarding domestic ring main socket circuit calculations im hoping i could get help with.

1) regards calculating I[SUB]t[/SUB]from table 4D5 in the regs it states that in order to use 2.5mm conductors that it should have a max value of 27A (ref method C), im unsure how to get this figure as I[SUB]n[/SUB] is going to be 30 or 32A. The only correction factor applicable is Ca which in this case is 0,94 so as i understand it i[SUB]t[/SUB]=i[SUB]n[/SUB]/correction factors =30/0.94 =31.9A. Obviously i understand it is common practice to 2.5mm cable, im just wondering how to prove this on paper.

2) regards volt drop in a ring main, i have heard conflicting theories about how to calculate this so was just wondering how other people would go about this?

Any help is very much appreciated
 
For the first part of your question have a read of reg 433.1.103 that Iz only has to be 20amp

The volt drop part I have always used the calc

Divide the length by 4 so for a 60mt RFC it would be = 15 x 18 x 26/ 1000

Bs 7671 pg 258, 6.1 corrections for operating temp.

This calculation give you a ct of .923

I was taught to assume 20 amp at the furthest point and 12 amp distributed evenly around the ring so,

average = (32 + 20)/2 = 26 which is the Ib
 

Reply to Ring main calculation help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
986
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
678
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
769
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock