In line with EU practice, Dual pole MCB's and radial circuits will halve the time taken for inspections and fault finding.

Dives for cover. :innocent: :eek:

Does EU practice mandate that radial circuits run simply from point to point? If any branches are permitted then surely inspection and fault finding becomes less straightforward.

I ask this because I remember reading about some European countries where it was common to find radial circuits that branched off in many directions - sort of like a tree.
 
I stayed in a Spanish rental for 2 weeks on holiday.
All the lightning circuits were just a single run of live, looped round all the switches.
The switched lives went off to there respective light pendants and instead of running a neutral to the fittings, they just connected the neutral of the fitting to the nearest bit of structural metalwork
 
I stayed in a Spanish rental for 2 weeks on holiday.
All the lightning circuits were just a single run of live, looped round all the switches.
The switched lives went off to there respective light pendants and instead of running a neutral to the fittings, they just connected the neutral of the fitting to the nearest bit of structural metalwork
At what voltage?
 
[ Citation required ]
Hi Guys. Just wanted to say I have read your replies so far with interest.This morning am a bit tied for time and want to give a reply to
Advantageous in what way?


Is this part of a move to closer alignment with EU wiring practice (similar to your T&E going for equal-size CPCs)?

Or any other specific reason(s) for the preference?
I am not aware of any moves to reduce use of rings in order to more closely harmonise with Europe (the increased size of the CPC in t&e was I understand). I think the appeal of the radial over the ring swung the balance. I personally find them simpler from an installation and testing point of view. The wiring saved in the omitted leg of the ring in many cases pays for the extra mcb. The customer now has 2 circuits of 20 amp rather than 1of 32. Radials not easily overloaded.
What's not to like?
[automerge]1596457633[/automerge]
Ok now you've got my dander up! Ring circuits will probably disappear eventually. But the reason is not some technical reason it is because of the dumbing down of the population in general. As regards the origins of the ring circuit it was maybe ahead of it's time ecologically as it was to save copper, ergo the natural environment. As you know I am an advocate of the ring circuit as per the other thread you referred to. Perhaps you are an agent provocateur insidiously dripping non reasons for getting rid of the ring circuit? It seems you don't like them with a vengeance. Which is a bit strange not to be dispassionate about a bit of wire and solely concentrate on the science and reasoning of each circuit type. Both have their merits and application, you just jolly well leave our ring circuits alone chappy.;)
Interestingly I was on a forum here locally for Irish sparks (cost me 50 euro) and tried to start a debate on some areas of Irish work practices which I felt (still do) could be upgraded. I pointed to the UK and basically said "they are ahead of the curve here, could we learn from that?" The reactions?? Take a guess. I think it's understandable we all get a little protective about our own regs and work practices.
One post kindly suggested I move to the UK.
I think to move forward its important to stand back and look objectively at the accepted norms whatever in whatever environment we are in and ask "is this still acceptable".
Now the ring circuit is in fact a very innovative wiring system which cleverly made use of limited resources getting the maximum out of the minimum of copper. In my view it still has a role to play but in a limited role. By the way my use of the word" dinosaur " was disrespectful and I did, nt intend that.
[automerge]1596457981[/automerge]
Does EU practice mandate that radial circuits run simply from point to point? If any branches are permitted then surely inspection and fault finding becomes less straightforward.

I ask this because I remember reading about some European countries where it was common to find radial circuits that branched off in many directions - sort of like a tree.
I have worked on radials in several countries and they all followed the same loop in, loop out system. To branch of off like a tree is not a system I have seen, but even if they did remember that a radial is never vulnerable to overloading in the way a ring is
[automerge]1596458310[/automerge]
I support and endorse the ring final circuit.
That's fine Risteard. Do you also still "support and endorse" the installation of a 4ft earth rod (as we are both required to install under Irish regs) but as has been demonstrated here on this forum by multiple sparks in multiple posts is actually less than useless?
[automerge]1596459002[/automerge]
As far as I know Spain is 220/230v @ 50htz.
The cotinent all tends to be somewhere between 220 and 240 at 50htz
[automerge]1596459227[/automerge]
I stayed in a Spanish rental for 2 weeks on holiday.
All the lightning circuits were just a single run of live, looped round all the switches.
The switched lives went off to there respective light pendants and instead of running a neutral to the fittings, they just connected the neutral of the fitting to the nearest bit of structural metalwork
That really surprises me. I also stayed in one last year and like you can't resist having a good look at the electrics. I don't open anything up but it looked top notch. Rcbo, s on every circuit too.
Obviously the light switch and inevitable socket in the bathroom but quite honestly I think we here (British Isles) have a, thing or 2,to learn from them here. Now as Mike said "dive for cover"
[automerge]1596459373[/automerge]
In line with EU practice, Dual pole MCB's and radial circuits will halve the time taken for inspections and fault finding.

Dives for cover. :innocent: :eek:
You are spot on here in my view. Did you mean rcbo, s when you mentioned dual pole mcb, s?
[automerge]1596459736[/automerge]
Does EU practice mandate that radial circuits run simply from point to point? If any branches are permitted then surely inspection and fault finding becomes less straightforward.

I ask this because I remember reading about some European countries where it was common to find radial circuits that branched off in many directions - sort of like a tree.

If this "branches of a tree" system interferes in any way with the standard wiring method for a radial circuit, then yes, that would complicate faultfinding. However, while circumstances, might occasionally require a JB to be I stalled between to sockets to branch off for a third, this would be an exception rather than the rule in my exp.
 
Last edited:
Dual pole MCB's are just that, it would need an RCB as well for the row of MCB's, but you can use multiple RCBO's instead and not need the RCB.
 
I have worked on radials in several countries and they all followed the same loop in, loop out system. To branch of off like a tree is not a system I have seen, but even if they did remember that a radial is never vulnerable to overloading in the way a ring is
[automerge]1596458310[/automerge]


If this "branches of a tree" system interferes in any way with the standard wiring method for a radial circuit, then yes, that would complicate faultfinding. However, while circumstances, might occasionally require a JB to be I stalled between to sockets to branch off for a third, this would be an exception rather than the rule in my exp.

I know little of the practices employed in other countries - in fact I have limited knowledge of UK practices and hoover up information where it is available - but had read threads that mentioned some fairly complex radial circuits. These may have been in very old properties and not the sort of circuit conventially installed, but the subject of easier inspection and testing was raised and I thought it a reasonable question to ask.

The radial/ring debate is something of a fascination for me and my untrained mind can see benefits and drawbacks to both. In general I tend to prefer the idea of radial circuits, but can also see instances where a ring seems the more practical option - one example would be a kitchen or utility room that houses multiple power hungry appliances. Even with the application of diversity there is a good chance of washer, dryer, dishwasher and kettle being used at once and potentially overloading a 20A radial, which I guess is why those rooms tend to be fed from a 32A breaker. Unless my understanding of BS 7671:2018 is flawed, a 32A radial, which is buried in plaster (or conduit in plaster) would need to be run in 6mm and not particularly convenient from the perspective of installation?
 
I know little of the practices employed in other countries - in fact I have limited knowledge of UK practices and hoover up information where it is available - but had read threads that mentioned some fairly complex radial circuits. These may have been in very old properties and not the sort of circuit conventially installed, but the subject of easier inspection and testing was raised and I thought it a reasonable question to ask.

The radial/ring debate is something of a fascination for me and my untrained mind can see benefits and drawbacks to both. In general I tend to prefer the idea of radial circuits, but can also see instances where a ring seems the more practical option - one example would be a kitchen or utility room that houses multiple power hungry appliances. Even with the application of diversity there is a good chance of washer, dryer, dishwasher and kettle being used at once and potentially overloading a 20A radial, which I guess is why those rooms tend to be fed from a 32A breaker. Unless my understanding of BS 7671:2018 is flawed, a 32A radial, which is buried in plaster (or conduit in plaster) would need to be run in 6mm and not particularly convenient from the perspective of installation?
4MM2 MATE, ,
 

Reply to Ring main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
921
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
239
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
404
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
251

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock