In the New Year I'm re-wiring an empty 3rd floor apartment. Now this has concrete floors and ceilings and very decorative ceiling coving to all rooms that have 'not to be disturbed'. A good solution for new cable runs would be behind the skirting boards and door architraves. This isn't mentioned as a safe zone in the Guide but is there a reason why I can't do this? Am I missing something obvious as to why I cant? The CU, obviously, will be dual RCd 17th Edition.
 
If the depth is less than 50mm, then you will need to use a cable with an earthed sheath, earthed conduit or trunking or provide mechanical protection.
Using an RCD isn't an option unless you consider it provides the same degree of safety as would be provided by compliance with BS7671, in which case you would have to note it as a departure.
 
I would imagine that another potential problem will be chippies banging big nails through your cables whilst fitting the skirting etc, unless you tell them to use alternative methods of fixing.
 
In the New Year I'm re-wiring an empty 3rd floor apartment. Now this has concrete floors and ceilings and very decorative ceiling coving to all rooms that have 'not to be disturbed'. A good solution for new cable runs would be behind the skirting boards and door architraves. This isn't mentioned as a safe zone in the Guide but is there a reason why I can't do this? Am I missing something obvious as to why I cant? The CU, obviously, will be dual RCd 17th Edition.

with rcd protection you can run in safe zones or horizontally/vertically direct to accessories or CU (OSG page 60)
 
In the New Year I'm re-wiring an empty 3rd floor apartment. Now this has concrete floors and ceilings and very decorative ceiling coving to all rooms that have 'not to be disturbed'. A good solution for new cable runs would be behind the skirting boards and door architraves. This isn't mentioned as a safe zone in the Guide but is there a reason why I can't do this? Am I missing something obvious as to why I cant?As previously stated unless you use a wiring system with an earthed outer sheath it wont comply.Stick to the safe zones. The CU, obviously, will be dual RCd 17th Edition.
.............
 
If the skirtings are coming off,then fit some conduit behind them

The chances are, a lot of covings may have a gap at the top which you could use
Given that there are concrete ceilings and the coving has to be untouched
How do you intend getting to the lights,is there existing conduit?
 
In my eyes way to risky one way you could do it would be to use some skirting trunking ,and architraves i think its manufactured by MK but may be mistaken
 
in a building like that, isnt the wiring run in steel conduit, further investigation may uncover some junction boxes that that conduit runs to. possibly in the airing cupboard etc once they are found, its just a matter of pulling through using existing wiring and single strand cable
 

Reply to Safe zone? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
918
So, I'm having grid switches in my new kitchen for things like cooker hood, dishwasher, fridge freezer, integrated microwave etc...and know how to...
Replies
6
Views
3K
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
909
I'm in the process of renovating a 1970's bungalow with a garage underneath. The electrical consumer unit is in the garage and there are multiple...
Replies
12
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock