L

Learning to Spark

So, I'm having grid switches in my new kitchen for things like cooker hood, dishwasher, fridge freezer, integrated microwave etc...and know how to wire up the switches and sockets as part of a ring final...

But my question is regarding how to route the cables from the above counter grid switches to the under counter/ behind unit, unswitched sockets, while keeping within the regs regarding safe zones.

Is it permitted to run vertically from the switches to appliance socket height, below counter or behind a unit and then form an L shape and run horizontally to the unswitched socket?? Or do I need to route cables up and along the ceiling safe zone and back down, even tho the appliance socket will be below the counter and behind the appliance, thus not immediately visible??

What's the best way to run this??
 
TL;DR
How do I route cables from grid switch to under counter unswitched socket while staying in safe zones?
L-shape, go down from the grid switch, then horizontally at the height of the sockets.

There are many online resources showing a diagram of zones within a room.
 
L-shape, go down from the grid switch, then horizontally at the height of the sockets.

There are many online resources showing a diagram of zones within a room.
I've been looking and because sockets wouldn't be visible I wanted to double and triple check... im still doing my 2365 but wanted to know how to do it within the regs. Thanks tho. L shape is what I thought.
 
You’re only interested in the switches and sockets on the wall…. Doesn’t matter if someone then hides the socket behind a washing machine or whatever.

You do get overzealous kitchen fitters that may not look where sockets etc are, but you can’t plan for idiots.
 
You’re only interested in the switches and sockets on the wall…. Doesn’t matter if someone then hides the socket behind a washing machine or whatever.

You do get overzealous kitchen fitters that may not look where sockets etc are, but you can’t plan for idiots.
That's all I wanted to know... because it will be behind the machine or a kitchen cabinet I want sure if that changed things. I fully understand the normal principles of safe zones on flat walls but never tried a kitchen before. Wanted to check and double check before things get ripped out for being wrong. Lol
 
If you follow the example given by @littlespark the isolator provides a safe zone for vertical cable drop and socket provides safe zone for hoizontal run.

Obviously this provides no guarantee that safe zones will be observed by anyone coming behind you, but it does mean you have discharged your obligations to ensure all cables are suitably routed.
 
If you follow the example given by @littlespark the isolator provides a safe zone for vertical cable drop and socket provides safe zone for hoizontal run.

Obviously this provides no guarantee that safe zones will be observed by anyone coming behind you, but it does mean you have discharged your obligations to ensure all cables are suitably routed.
This is exactly what I needed to know. I am putting steel capping over the cables anyway, but wanted to make sure they are compliant without the requirement to be earthed, as I doubt the capping would protect against a drill.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Kitchen Grid switches and safe zones
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Learning to Spark,
Last reply from
Learning to Spark,
Replies
6
Views
3,626

Advert