Justinsane

Hi, a customer of mine phoned me the other night to say she had just touched the water inlet pipe to the shower and had a shock off it (she was in the shower at the time!)

I've been and looked at the job today and can't work out what is going on. I get a reading of 1 - 2 volts off the pipe whilest the shower is on. I also get this reading at different points on the pipework around the house.

Nothing when the shower is off. Surely this shouldn't happen but I wouldn't have thought she could get a shock off it....

I've check the bonding, its a TT system where a new c/unit has been run from the existing supply and the earth rod has been connected to the new box and then ran back to the old one. The installation is on a 100amp voltage controlled breaker and the shower circuit is on a 40amp mcb from the new box which has an RCD main switch. All pipework is bonded.

The loop reading from the shower is 181ohms.

Anyone got any ideas whats happening and why nothing is tripping....

cheers,
Justin
 
Firstly, where does the earth wire go from the old box ? - This sounds a bit strange on its own. First Job in that house is to do a continuity on the main Earth and bonding conductors. After completly isolating the shower of course. R1 +R2 of the shower circuit as Well. Have the front off the shower, you may find the answer stairing you in the face, however, there are further problems with this installation.
 
I have taken the front off the shower and the reading off the pipe was taken between the pipe and the neutral on the shower, (is this the correct way to test this?) Someone from the distribution company called by and took the readings from the other pipework using a clampmeter.

The original earth is a thin green cable which comes from the main breaker and would have originally been connected to an earth rod outside what was once the back door. When the extension was built this earth rod has been moved. A new c/unit was installed in the new extension fed from a 16mm submain from some henleys at the main box. The earth rod has been connected to the new c/unit and the old thin green earth wire has been connected to a new piece of wire and then into the new c/unt. Also a new earth cable has been run from the old unit to the new one. The bonding to water and gas is also connected to the new c/unit thus making this the main earthing terminal...it seems a weird way of doing things to me.
 
So the old unit, feeds circuits in the old part of the house, the new unit is in the extension, Rodded, and the old unit is also rodded, correct ? - is there an old voltage operated breaker at the old board ( get that out !) and which board does the shower run off. Please give a bit more detail where you say the earth wires appear to be joited, thick to thin. It appreciate this is all hard to describein words mate !!
 
The main supply comes into the house where it comes from the meter through a 100amp voltage controlled breaker. 3 small green earth cables also come out of the consumer side of this breaker. 1 goes to the old fuse box, 1 goes to an old economy 7 unit which is not used (all the points have been disconnected around the house). and the other goes to the other side of the house where the extension has been built where it has been pushed up into the attic and joined to a 10mm (i think) earth cable with a terminal block and run to the new consumer unit in the extension.

The old consumer unit supplies the kitchen, bedrooms, main bathroom (without shower) and living rooms.

The extension was built to provide one bedroom and a shower room both supplied from a 5 way RCD main switch consumer unit.

The earth rod (there is only one) has been moved to out side the new extension and is connected straight back to the new c/unit where the older earth cable has been terminated (via its extension to a thicker cable)

There are two henley blocks splitting the l and n to a main switch which feeds the extension unit via a 16mm cable.

There is also a new earth cable run from the old c/unit to the new unit.

Bonding to the gas and water is connected to the new unit in the extension.

The wiring in the old house is old and messy. I have mentioned rewiring the old house but the customer doesn't want the expense, they just want it safe....I'm not sure I can do one without the other....

I tested earth loop from the shower itself and got a reading of 181 but not sure if this was through the pipework or the rod.

I need to go back and test all the bonding and main earth as you said.

Would this current be leakage from the shower?
The shower circuit is all new and fed from the new board with an RCD.

Are the old voltage controlled breakers dodgy?

I was going to suggest ripping out the old box and the economy 7 box and installing a new time delayed main switch supplying a new unit and the extension unit. Along with new earth rods for both c/units..

Is it possible to get the system upgraded to a PME? I have seen a couple of TT systems where they have literally split the neutral via a henley block and run an earth cable into another henley making that the MET and stuck a PME sticker on it...
 
First thing you need to do is check the main bonding, equipotential bonding and supplementry bonding ,
once you have that sorted test the operation of the RCD.
If the wiring is that bad do a PIR , but by the visual report you've given sounds like a rewire.
 
If there is a voltage operated ELCB it should trip if you do an earth loop on the shower....does it trip on the test button? Sounds to me like there is an earth fault somewhere on the installation and the failure of the main earth fault protection( ELCB) to operate is causing a voltage to appear on extraneous and conductive parts. You need to do an IR test on all circuits and clear any low readings and install an acceptable method of earthing.
 
The ELCB test button works but it didn't trip when I took the earth loop reading from the shower.
I tested the RCD on the new unit and it is fine.

The customer can't afford to pay for a rewire.

I suspect the problem is coming from the shower, but don't know why it isnt tripping.
Even if there isnt earth continuity on the pipework back to the box it should still trip shouldn't it?
A lot of modern installations use plastic pipes where the only bonding is at the entrance points to the building so showers , baths, sinks etc aren't bonded anyway.

There is an earth link within the shower itself between the cpc and the pipe.
 

Reply to Shock off shower in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
263
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock