hello guys

I quite often find that when terminating 25mm tails into a 100a fuse board isolator you do not get the 25mm tails to squash nicely by the main switch thermals like you would 16mm tails, should be be using copper blade terminals instead to ensure a better connection?
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Pete999

-
Arms
Esteemed
hello guys

I quite often find that when terminating 25mm tails into a 100a fuse board isolator you do not get the 25mm tails to squash nicely by the main switch thermals like you would 16mm tails, should be be using copper blade terminals instead to ensure a better connection?
Explain please, a picture of what you are suggesting will help.
 

Pete999

-
Arms
Esteemed
Thanks Westy
hello guys

I quite often find that when terminating 25mm tails into a 100a fuse board isolator you do not get the 25mm tails to squash nicely by the main switch thermals like you would 16mm tails, should be be using copper blade terminals instead to ensure a better connection?
From Westies info then no unless the terminals are designed for flat cables imo
 
T

Toneyz

You shouldn't need to if as I think you are referring to a domestic consumer unit 100A main switch it should be designed to take 25mm tails.
 

Andy78

-
Mentor
Arms
Esteemed
No problem using 25mm tails. Just form them properly, set them in the terminals, then re-tighten after they have settled a bit.
If problems persist try an extra weetabix in the morning.
 
T

Toneyz

No problem using 25mm tails. Just form them properly, set them in the terminals, then re-tighten after they have settled a bit.
If problems persist try an extra weetabix in the morning.
Or have three shredded wheat for breakfast with spinach for the evening meal.
 
You shouldn't have problems terminating 25mm tails into a switch. If you are then you are doing something wrong.

You need to use your hands and form the cable correctly so it simply drops into place without putting strain on the switch and then tighten.
 
S

Squid

Takes me back many years using a hydraulic crimper on 400 mm SWA.
 

telectrix

-
Mentor
Arms
Esteemed
aaaaaaaaany decent scouser would have nicked the hydraulic tool and flogged it before you could finish your tea.:D:D:D
 

davesparks

-
Mentor
Arms
Esteemed
Using 19 strand tails instead of 7 strand can help a lot with this, they are much more flexible and easier to work with.
 

mattg4321

-
Arms
Esteemed
Using 19 strand tails instead of 7 strand can help a lot with this, they are much more flexible and easier to work with.
Be careful as some DNO don't like this. UKPN didn't recognise the 19 strand tails as acceptable when I last enquired. This may have changed now though.
 

davesparks

-
Mentor
Arms
Esteemed
Weston Power say no to Tri rated into their cutouts.
As do most DNO's and I think it extends to any sort of flex, not just tri rated. But the 19 strand tails I suggested are not flex, they are just 19 strand insulated and sheathed singles.
 

davesparks

-
Mentor
Arms
Esteemed
Be careful as some DNO don't like this. UKPN didn't recognise the 19 strand tails as acceptable when I last enquired. This may have changed now though.
That's odd considering most DNOs and metering companies seem to use them these days.
 