Hi. I'm a new user to this forum, and would appreciate if you could help me out on this one.

i need to price a job on a new shower block. Customer has just had new three phase supply. Shower block is 100metres away from DNO cut out.

I was thinking of


4 pole 300ma TD RCD in an insulated enclosure
100A metal fused switch disconnector TP&N
100m of 25mm 4 core SWA cable
square d 3 phase db with 125a main switch

Can anyone suggest a good, spacious Insulated rcd enclosure?! Also, does anyone see any problems with this setup!?

Thanks for your help
 
You may need to consider several other factors as well. Volt drop and earthing system(s) and bonding comes to mind first. Then location of distribution, final circuit protection. Isolation, cable route, zoning, installation methods, demand, environment. Most people on this forum will gladly offer advice and suggestions, but a free design service may be stretching the point :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
shower block- new three phase supply
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Johnmillington,
Last reply from
High Tower,
Replies
4
Views
2,284

Advert